    How do you charge a R410a inverter split?



    Hi guys,

    I have possibly a simple question,

    But how do you charge an inerter split system? Im guessing it's quite hard to over charge one of these systems. But i have to add gas to a system that is short, due to someone extending pipe runs. Do i have to weigh the gas in with the calculations of the extra metres of pipe?

    Thanks in advance



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: How do you charge a R410a inverter split?

    In short, yes, always remove any old charge and weigh in the correct amount.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: How do you charge a R410a inverter split?

    best to refer to manufacturers recommendations, measure the piperun, the factory charge will be upto x distance, any extra pipework is usually charged at 30grm per meter- but refer to the installation guide, then label the unit of system charge.

  4. #4
    Join Date
    Jul 2009
    Location
    Australia
    Age
    33
    Posts
    16
    Rep Power
    0

    Re: How do you charge a R410a inverter split?

    Ok thanks. But for an inverter do you need to run the system flat out on cooling or just half way. So it ramping at full capacity or only half.

  5. #5
    Join Date
    Jul 2009
    Location
    Australia
    Age
    33
    Posts
    16
    Rep Power
    0

    Re: How do you charge a R410a inverter split?

    Of course, if you work out the calculations, it doesn't matter how you run it, because you know the exact amount. But what if you're just topping it up?

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: How do you charge a R410a inverter split?

    charging of a split is critical, its easy to over charge, as the compressors are usually inverter driven and electronic expansion valves modulating to match the demand your pressures will fluctuate, weigh out the remaining gas, you have to pressure test with nitrogen to repair the leak then recharge

  7. #7
    Join Date
    Jul 2009
    Location
    Australia
    Age
    33
    Posts
    16
    Rep Power
    0

    Re: How do you charge a R410a inverter split?

    Quote Originally Posted by install monkey View Post
    charging of a split is critical, its easy to over charge, as the compressors are usually inverter driven and electronic expansion valves modulating to match the demand your pressures will fluctuate, weigh out the remaining gas, you have to pressure test with nitrogen to repair the leak then recharge
    Let's say, i don't have a reclaim unit. And on install, the installers added extra pipe length but didn't add any refrigerant to accomodate. I'm going to this job to top up the gas to make it run sufficiently as the cooling is poor.

  8. #8
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: How do you charge a R410a inverter split?

    you could try it, depends if the system has ever worked properly, if it worked ok then its lost performance then theres probably a leak on it

  9. #9
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    49
    Posts
    412
    Rep Power
    23

    Re: How do you charge a R410a inverter split?

    Quote Originally Posted by Brian_UK View Post
    In short, yes, always remove any old charge and weigh in the correct amount.
    dear brian,

    is subcooling not relevant to findout the proper charging for R410a system?samelike the calculation of ambient temp+30f is the maximum saturated discharge temp.

    moideen-dubai

  10. #10
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: How do you charge a R410a inverter split?

    its too inaccurate, the lev start up in an initial mode,after 5-10 minutes then it starts to operate modulating as req, also the the compressor frequency is trying to ramp up to reach setpoint, it can be done but with aussie gas prices its probably cheaper to buy a new system

  11. #11
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: How do you charge a R410a inverter split?

    Quote Originally Posted by AC noob View Post
    Let's say, i don't have a reclaim unit. And on install, the installers added extra pipe length but didn't add any refrigerant to accomodate. I'm going to this job to top up the gas to make it run sufficiently as the cooling is poor.

    If you don't have the correct tools to do the job, don't do it. Either purchase them or leave the work to better equiped technicians.

    How do you know its just under charged from new and not under charged and also leaking without testing for leaks?

    Sometimes a system only needs another 20g or so, you will not see any change on your gauges with this amount so how do you expect to get anywhere near the correct charge without weighing it in as per manufacturers specs.
    Mostly found in Oxfordshire, UK :)

  12. #12
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: How do you charge a R410a inverter split?

    Quote Originally Posted by moideen View Post
    dear brian,

    is subcooling not relevant to findout the proper charging for R410a system?samelike the calculation of ambient temp+30f is the maximum saturated discharge temp.

    moideen-dubai
    As many have said already, with these critical charged units the correct weight of refrigerant is the only way to go especially with inverter drives.

    I recently had a small split, inverter, with reasonable superheat but which would suddenly loose the superheat as the expansion valve tried to compensate for a shortage of refrigerant; 300g out of 1.5kg it turned out to be short.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  13. #13
    AussieFridgie's Avatar
    AussieFridgie Guest

    Re: How do you charge a R410a inverter split?

    If there is doubt about whether the additional charge was not added, or if it was (maybe) lost, you have to scrap it, R410a is a blend Noob, if some of it has been lost it doesn't work that well anyway. Better for your customer to start from scratch with the manufacturers guidelines and go from there, otherwise you could overcharge. Also weighing in the charge means you can eliminate over or under charged as a cause of any problems.

  14. #14
    Join Date
    Dec 2008
    Location
    Brazil
    Posts
    106
    Rep Power
    16

    Re: How do you charge a R410a inverter split?

    You guys are talking about TEV. Do you mean R410A mini-splits as Samsung and LG also use TEV, instead of a capillary tube or other fixed devices ?

  15. #15
    Join Date
    May 2010
    Location
    West Sussex
    Age
    34
    Posts
    5
    Rep Power
    0

    Re: How do you charge a R410a inverter split?

    Quote Originally Posted by AC noob View Post
    Of course, if you work out the calculations, it doesn't matter how you run it, because you know the exact amount. But what if you're just topping it up?
    Topping up........ #illegal you can't just top up! You need to reclaim the gas! Measure the pipe run and work out the correct charge. Then vac the system and charge it! You should get all the gas in under a vac! The compressor being an inverter or fixed speed doesn't matter

  16. #16
    Join Date
    Oct 2004
    Location
    essex england
    Age
    49
    Posts
    10
    Rep Power
    0

    Re: How do you charge a R410a inverter split?

    The term "topping up" doesnt sit well with me...

  17. #17
    Join Date
    Jun 2010
    Location
    Yorkshire
    Age
    59
    Posts
    520
    Rep Power
    19

    Re: How do you charge a R410a inverter split?

    If it has got a leak and not cooling, then it could have lost a considerable amount to cause fractionation, it isn't unheard of with blended refrigerants that have lost substantial amounts. In which case you might be better to reclaim and leak test, repair the leak if you find one. Then re gas with a fresh charge, this could iron out any problems with the system not working correctly, and you having to return and scratch your head trying to find faults that aren't there.

    Or if its a new install and the charge in the system isn't sufficient for the extra run, then you shouldn't need to reclaim unless there is a leak. And I've just realised that this post is a month old so you've probably sorted it by now.
    Training may be finished but experience is never complete.

  18. #18
    Join Date
    Jun 2010
    Location
    simferopol
    Age
    69
    Posts
    2
    Rep Power
    0

    Re: How do you charge a R410a inverter split?


  19. #19
    Join Date
    Jun 2010
    Location
    Yorkshire
    Age
    59
    Posts
    520
    Rep Power
    19

    Re: How do you charge a R410a inverter split?

    Quote Originally Posted by alexaso View Post
    Yes that's true in most cases, but has anyone ever been to a job and ended up topping off near azeotropes after a sustantial leak only to find that the system doesn't work properly. And you end up fault finding and getting no where and giving yourself a headache, only after a while you decide to decanter and recharge with fresh and find the system performs better?
    Training may be finished but experience is never complete.

  20. #20
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: How do you charge a R410a inverter split?

    Have I missed something here??? The noob said he has to add gas due to additional paperwork on installation.
    So as I see it, calculate additional charge run unit on cooling and lob it in job done, label it up and go to the pub...
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  21. #21
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: How do you charge a R410a inverter split?

    additional paperwork!!!-yep it can be a pain in the arse!- if your referring to additional pipework then he should reclaim to prove he has the factory charge within the system, if it aint labelled,system charge then you cannot guarantee that additional was added and its leaked
    Quote Originally Posted by stufus View Post
    Have I missed something here??? The noob said he has to add gas due to additional paperwork on installation.
    So as I see it, calculate additional charge run unit on cooling and lob it in job done, label it up and go to the pub...
    Cheers
    Stu