    Hey guys my second question is when checking AMP Draw comparing to Full Load AMP. Is this a accurate way of checking for overcharge? Because I have seen techs out there overcharging the system and the AMP Draw still look less than FLA. I understand receivers sometimes are oversized so a little overchage wont be effected. So does this mean I can always just go by AMP DRAW and charge the unit until it hits FLA ?
  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51
    Re: How to Check Charge with AMP Draw?
    Got to agree, but watching the amp draw while charging can tell you a great deal.
    Under charged and low amp draw in relation to nameplate rating, over charged and high amp draw etc.
    Always have a clamp meter on when charging - even if you have calculated the additional charge for a VRV system. It lets you know the state of the compressor.
    I've watched "young techs" charging to suction pressures in low ambient conditions and wondering why they can't achieve decent "back pressures" - without monitoring amp draw
  3. #3
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    744
    Rep Power
    25
    Now that we are discussing "pushing in the contactor".
    I know an engineer who doesn't own a recovery machine, he just connects his liquid line to a bottle and "shoves in the contactor"
    Does this work properly?
    Please discuss.
    cheers
    eggs
  4. #4
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    744
    Rep Power
    25
    oooops wrong thread, can it be moved please?
    cheers
    eggs
    should have been the schraider removal thread.
Similar Threads
  1. Air conditioning maintenance procedure
    By Andy T in forum Air Conditioning
    Last Post: 27-05-2006, 06:57 PM
  2. Calculating refrigerant charge
    By Consultant in forum Refrigerants
    Last Post: 10-05-2005, 03:39 PM
  3. Double check needed
    By Latte in forum Trouble Shooting
    Last Post: 11-08-2004, 12:46 PM
  4. Compressor Check for locked rotor voltage
    By shogun7 in forum Trouble Shooting
    Last Post: 04-04-2004, 12:44 AM
  5. How do you charge a car A/C
    By dude in forum Air Conditioning
    Last Post: 02-04-2004, 09:36 AM
Posting Permissions
  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts