    Question Akv



    Hi ,

    I m new in this field and i needt to know ,

    Can I use AKV in plug-in cabinets ?



  2. #2
    Join Date
    Dec 2007
    Location
    ireland
    Age
    54
    Posts
    275
    Rep Power
    26

    Re: Akv

    You really should contact danfoss to get information on this. If using on a small plug in i would imagine the valve pulsing might have to be lowered to obtain steady regulation . Perhaps a spindle type electronic valve would be more suitable.

  3. #3
    Join Date
    Jun 2002
    Location
    UK
    Posts
    628
    Rep Power
    23

    Re: Akv

    Quote Originally Posted by koraygfb87 View Post
    Hi ,

    I m new in this field and i needt to know ,

    Can I use AKV in plug-in cabinets ?
    No I am afraid not
    they dont mind supermarkets where compressor packs, and display cases are used..

  4. #4
    Join Date
    Jan 2013
    Location
    Turkey
    Posts
    3
    Rep Power
    0

    Re: Akv

    Why can not use AKV?

  5. #5
    Join Date
    Jun 2008
    Location
    NZ
    Posts
    102
    Rep Power
    17

    Re: Akv

    Gordon Bennett.

    Years ago, I installed a display model of a cabinet with an AKV fitted by the OEM in a showroom in Harlow.

    When we commissioned it, the client asked: "What's that horrible noise"... AKV out, TEV in... never been a fan of pulse valves since then...

    I guess, if valve sizing and system design is correct, an AKV *should* work, but a TEV would be more economical in terms of initial cost.