    Schrader valve renewal



    Hi.

    Basically I have a discovered a leak after removing the schrader valve cap on the suction side of an old Toshiba R22 split.

    I have a core removal tool and spare cores, just wondering what is the best way to go about repairing the valve, i.e will I have to recover before taking the core out or is there a way around it?

    Thanks in advance.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Schrader valve renewal

    You can change the valve with this tool when the system is charged. http://www.hawco.co.uk/refrig/Sectio...Section6_1.htm

    Last item on the page

  3. #3
    rbartlett's Avatar
    rbartlett Guest

    Re: Schrader valve renewal

    pump it down..

    cheers

    richard

  4. #4
    Join Date
    Dec 2005
    Location
    Cheshire
    Age
    39
    Posts
    264
    Rep Power
    21

    Re: Schrader valve renewal

    Quote Originally Posted by frank
    You can change the valve with this tool when the system is charged. http://www.hawco.co.uk/refrig/Sectio...Section6_1.htm

    Last item on the page
    Noticed this tool in HRP and SRW also, was tempted but cannot understand how I would actually attached it onto the leaking valve thread without refrigerant escaping alot/getting burnt!

  5. #5
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Schrader valve renewal

    Frank,

    That looks like a very useful tool. I have not seen one of these, but then I have not had to work on any schrader valves for a long, long time.

    It does seem to take all of the fun out of doing a hot change-over on a liquid line though.

    Thanks for the info and heads-up on this tool.

  6. #6
    Join Date
    Dec 2005
    Location
    Cheshire
    Age
    39
    Posts
    264
    Rep Power
    21

    Re: Schrader valve renewal

    Quote Originally Posted by rbartlett
    pump it down..

    cheers

    richard
    Thought about that too, havnt got the model number on me, its a 7kw ceiling suspended think about 1997 model, is there a forced cooling mode or will I have to trick it by warming the thermistor as its only about 12 degree c in the room.

    Apologies if there are a lot of questions, as you can prob tell I'm mainly installation!

  7. #7
    Join Date
    Mar 2004
    Location
    UK
    Posts
    624
    Rep Power
    21

    Re: Schrader valve renewal

    Hi

    This is a excellent tool and I use it often,its ideal when charging a pack as the shreader valve restricts the flow.You attach the tool on to the shreader threads then send the extraction rod in and remove the valve this is a sealed chamber,pull the rod back and close the shut off valve on the tool and unscrew rod and valve.

    Hope that makes sense

    Regards Bernard

  8. #8
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Schrader valve renewal

    If you are going to pump it down then just hook up the gauges, close the liquid line valve, stick the screwdriver on the contactor and then close the suction valve when the gauge reads 0psig 'nuf said

  9. #9
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Schrader valve renewal

    Quote Originally Posted by Slim R410a
    ..... is there a forced cooling mode .....
    Select Cool mode on the controller when in the Off condition, then press and hold the on/off button until an 'L' appears on the display; you now have about 30 minutes before it reverts to normal or you switch off again.

    You should also have in your PPE kit some heat (cold) resistant gloves shouldn't you ? Ideal for occasions like this.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  10. #10
    Join Date
    Nov 2005
    Location
    australia
    Posts
    152
    Rep Power
    19

    Re: Schrader valve renewal

    If you do not want to drop the charge

    Imperial make a tool (PINCH OFF TOOL 105-FF)

    here is the link

    http://www.stridetool.com/tools/hose...etools_01.html

    this tool pinches off your pipe cutting supply of refrigerant to the fan cycle , so you can replace
    without interference to the charge , when replaced it has rerounders of different diameters so you can reround your pipe and let refrigerant flow to the control.

    MANITOWOC recommend using this tool on their
    ice machines as to not interfere with the factory
    charge when changing their fan cycles.
    The primary function of the design engineer is to make things difficult for the fabricator and impossible for the serviceman.

  11. #11
    Join Date
    Jul 2005
    Location
    Ireland
    Age
    56
    Posts
    164
    Rep Power
    19

    Re: Schrader valve renewal

    HI Just get yourself one of the schrader extractor tools I've had one for years and its paid for itself many times over.
    T

  12. #12
    Join Date
    Jan 2006
    Location
    Port Adelaide
    Posts
    52
    Rep Power
    19

    Re: Schrader valve renewal

    I see on that link frank you pay 14 pound for a quik connector and 28 for the schrader tool. bargin. In Australia your up for $70.00 and $80-$90 respectivly.

    I've got one of each. Need 2. It was suggested in our training that these items should be compulsory in everyones tool bag to be accredited. Best practice for minimal refrigerant loss.

  13. #13
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Schrader valve renewal

    At todays exchange rate the core extract tool £28 would cost $aus 65.58 so a fair saving. Now, taking into account the postage and my handling fee it may not be such a saving for you

  14. #14
    Join Date
    Dec 2005
    Location
    Cheshire
    Age
    39
    Posts
    264
    Rep Power
    21

    Re: Schrader valve renewal

    Thanks for all the help.

    I will pump it down using forced cooling mode, if that fails will push in the contactor like said...

    I do have all the ppe etc

    Cheers,
    Last edited by Slim R410a; 16-11-2007 at 06:39 PM.

  15. #15
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Schrader valve renewal

    Some condensing units do not bring the fan on when you push in the contactor hence the warning sticker on them
    It's best to have the fan running when pumping down to ensure fluid phase change

  16. #16
    Join Date
    Feb 2005
    Location
    Aberdeen
    Age
    48
    Posts
    168
    Rep Power
    20

    Re: Schrader valve renewal

    Don't hold contactor in as this is incorrect procedure. I reckon Frank was only joking with you and as you said, you are more used to installation than service you will end up doing more damage to yourself than the air-con unit!
    Be safe at all times

    Jase

  17. #17
    Join Date
    Dec 2005
    Location
    Cheshire
    Age
    39
    Posts
    264
    Rep Power
    21

    Re: Schrader valve renewal

    Pumped it down using the forced cooling mode today with no problem at all. (Cheers Brian)

  18. #18
    Join Date
    Dec 2005
    Location
    Cheshire
    Age
    39
    Posts
    264
    Rep Power
    21

    Re: Schrader valve renewal

    Quote Originally Posted by frank
    Some condensing units do not bring the fan on when you push in the contactor hence the warning sticker on them
    Yes I have always noticed these stickers on the Mitsubishi R407c fixed speed range.....

    I learn something new everyday

  19. #19
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Schrader valve renewal

    Quote Originally Posted by Slim R410a
    Pumped it down using the forced cooling mode today with no problem at all. (Cheers Brian)
    Glad to hear that the problem is resolved.

    BTW if you want forced heating on a heat pump then select HEAT and press/hold the button again and an H will show this time. You don't get and fancy defrosting in this mode it will blow cold air inside!!
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  20. #20
    Join Date
    Jan 2006
    Location
    Port Adelaide
    Posts
    52
    Rep Power
    19

    Re: Schrader valve renewal

    Quote Originally Posted by frank
    At todays exchange rate the core extract tool £28 would cost $aus 65.58 so a fair saving. Now, taking into account the postage and my handling fee it may not be such a saving for you


    Gee Thanks Frank

  21. #21
    Join Date
    Dec 2005
    Location
    Cheshire
    Age
    39
    Posts
    264
    Rep Power
    21

    Re: Schrader valve renewal

    Quote Originally Posted by Brian_UK
    Glad to hear that the problem is resolved.

    BTW if you want forced heating on a heat pump then select HEAT and press/hold the button again and an H will show this time. You don't get and fancy defrosting in this mode it will blow cold air inside!!
    Whilst on the subject, what are the differences between Heat 1 and Heat 2 modes on these Toshiba's?

  22. #22
    Join Date
    Jan 2006
    Location
    Port Adelaide
    Posts
    52
    Rep Power
    19

    Re: Schrader valve renewal

    mmmm, yes Brian. Is it possible to purchace stem removers and quik couplers for R410A systems?

  23. #23
    Join Date
    Jan 2006
    Location
    Port Adelaide
    Posts
    52
    Rep Power
    19

    Re: Schrader valve renewal

    Quote Originally Posted by Marc O'Brien
    Mine doesn't do R410A connections?

    Found a R410a quik couler manufactured by REFCO. Part number V-3541015. I was told they don't exist. And I have seen both schader core remover and coupler. I'll get back with a part number on the former

  24. #24
    Join Date
    Dec 2005
    Location
    Cheshire
    Age
    39
    Posts
    264
    Rep Power
    21

    Re: Schrader valve renewal

    Ive had R410a quick couplers for ages, SRW do a set with a straight one and a 90 deg. one! Never had a cold burn since

Similar Threads

  1. Fitting an expansion valve question
    By Larry2 in forum Air Conditioning
    Replies: 20
    Last Post: 08-04-2008, 04:17 PM
  2. Scotsman commercial H2O inlet valve
    By fullcourt in forum Trouble Shooting
    Replies: 9
    Last Post: 25-04-2006, 11:41 PM
  3. Need a correctly sized valve
    By Abe in forum Commercial
    Replies: 2
    Last Post: 26-10-2005, 08:42 PM
  4. Replies: 5
    Last Post: 16-10-2002, 12:38 AM
  5. Valve "Hunting"
    By Abe in forum Trouble Shooting
    Replies: 20
    Last Post: 21-01-2002, 12:29 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •