Results 1 to 12 of 12
    May 2012
    8
    Compressor freezing up
    What is the cause of the compressor freezing up ie ice on the top of the compressor
    Any help would be appreciated
    Dave
    Feb 2007
    2,473
    45
    Re: Compressor freezing up
    Poorly adjusted expansion device...
    Feb 2008
    505
    21
    check the superheat to make sure no liquid returning to compressor
    Oct 2007
    manchester
    5,639
    45
    also check controls- thermostat ok, contactors not welded, evap coil clean,no ice build up on indoor coil,defrost works,all evap fans working
    11,025
    What is the operating temperature of the suction line and the dew point of the ambient air ?
    May 2012
    8
    Hello Brian
    I am a complete novice but find refrigeration interesting. I have adjusted the expansion valve TEX 5 this has cured the problem.
    I suppose screwing the adjustment in gives less superheat ie no liquid going back to the compressor.
    How do i check for superheat?
    Dave
    Oct 2007
    manchester
    5,639
    45
    Feb 2007
    2,473
    45
    One question...
    If you don't know how to measure superheat, how on earth did you adjust the TEV???
    Quick, call a professional before your compressor fails. (At least if your compressor serve a system you care about)
    Quote Originally Posted by Allen Key View Post
    Hello Brian
    Dave
    11,025
    Hello Brian
    Dave
    If you have to ask that question then what are you doing playing with the expansion valve?
    Next thread will be 'my compressor has seized up due to overheating' or similar.
    [edit]Sorry should have read down to see that the Viking has already raised the issue.
    Somerset
    69
    4,698
    Hi Allenkey.
    What my knowledgeable friends are trying to tell you in their own special way.
    Is adjust to far one way and you will flood liquid refrigerant back to the compressor and wreck it!
    Or overheat the comp and its motor with a seizure of either or both!
    Simply put you are playing with that which can easily be set incorrectly.
    Many so called experienced engineers do!
    So for everyone piece of mind.
    Don't do it!
    May 2012
    8
    Thats great mate thanks alot for the advice
    May 2012
    8
    Advice taken cheers for the info