    Dec 2006
    Indonesia
    Cold Storage for vegetables?
    Hi again from Indonesia I actually have two questions:
    1. I'm gonna build a cold storage room for vegetables with the dimension of 5m x 10m x 3.5m, initial temperature would be around 26°C and need to bring the temperature down to 10°C.
    How much compressor power do I need?
    And what system shall I use? Because from previous experience, using evaporator will result in drying the vegetables.
    2. I have a 1000 liter of water with the temperature of 80°C, would like to stabilise the temperature down to 40°C, how do I calculate the compressor power?
    Thanks in advance! Any help would be appreciate it.
    11,192
    Re: Cold Storage for vegetables?
    Contact a reputable system designer.
    If you had dry vegetables then your system was not designed or working correctly.
    Dec 2006
    Indonesia
    Thank you for your suggestion! I will definitely look into that.
    lebanon
    130
    hi adam
    for the dimensions of this room you need
    1-12 kw evaporator
    2-10 kw compressor capacity
    for your previous experience you need a bigger evaporator
    lebanon
    130
    hi adam
    for your second request you did not mention the time of the process
    any way a cooling tower can do this job
