    daikin REYQ16M8W1B inverter compressor not running?



    evening all

    (posting on a friday night! man i must be getting old! )

    back after some time in the wilderness new firm...new username... but same old daikin..tut

    got sent to a job today where a previous engineer had (very) recently reclaimed and re-gassed
    on a REYQ16M8W1B/r410a/factory charge:14.6kgs..approx another 5kgs by mr previous...?? he claimed it needed another 2.5kgs thats why it was underperforming?

    got to site and found all cassettes with poor off coil temps (average) across all 8 indoor units
    about 25c in full heating(bank full of women!)
    was informed "mr previous" had put a quote in for new inverter board/compressor the day before,after the re-gas.

    checked ohms and to ground (using multimeter)on all 3 comps and was confident there were no issues with all 3,nothing glaringly obvious id say.

    put gauges on at service ports an left them on for 30mins and got 25bar/360psi HP and 7bar/100psi LP suggesting it was a bit short and all controllers had E4 when pressing test button.

    considering it was cold and wet i saw no frosting on condensing coil,usually bottom half isnt it?then defros

    so i'm guessing an obvious undercharge or a leak still present in system?

    heres the stumper for me...i understand the inverter comp1(going from left to right in unit) will start up on first load through the inverter board and do its thing,then the following comp2 will come in on more demand and so forth to comp 3?

    also when on site only middle compressor was running and inverter comp idle? but no fault/outdoor safety activated like the older daikins(E0) when there I-boards went down?

    due to it pissing down with ice cold rain and fading light and 400v i beat i hasty retreat...
    daikin tech closed till monday,god bless them

    if anyone could point me in the direction of service manuals/settings or any info on troubleshooting them dam inverter boards i would be much obliged...

    ta



  2. #2
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: daikin REYQ16M8W1B inverter compressor not running?

    How much impuls on EEV 1-2 in outdoor unit? Same in indoor units... What loading in HZ of comressor, SC Sh and discharge SH

  3. #3
    Join Date
    Dec 2012
    Location
    LONDON
    Age
    44
    Posts
    14
    Rep Power
    0

    Re: daikin REYQ16M8W1B inverter compressor not running?

    like i said it was getting dark and raining only did a few checks..the EEV's were working because the 1/4" distributor pipe-work onto the outdoor coil was frosting?

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: daikin REYQ16M8W1B inverter compressor not running?

    maybe disabled inverter comp on setting modes on outdoor

  5. #5
    Join Date
    Dec 2012
    Location
    LONDON
    Age
    44
    Posts
    14
    Rep Power
    0

    Re: daikin REYQ16M8W1B inverter compressor not running?

    monkey you might be onto something there..
    common sense prevails again,will check that out m8.

    ta

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: daikin REYQ16M8W1B inverter compressor not running?

    I would agree with Monkey...check that the system is not programmed in Emergency Mode, which will inhibit the inverter compressor and give you the under performing readings you are seeing.
    Cheaper and quicker than reclaiming the charge.

  7. #7
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: daikin REYQ16M8W1B inverter compressor not running?

    for the records- Im not mr previous

  8. #8
    Join Date
    Dec 2012
    Location
    LONDON
    Age
    44
    Posts
    14
    Rep Power
    0

    Re: daikin REYQ16M8W1B inverter compressor not running?

    ha-ha
    ta mr monkey
    ta mr moderator

    sounds spot on....tedious internet search for manuals begins....

    mr p does worry me though!

  9. #9
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: daikin REYQ16M8W1B inverter compressor not running?


  10. #10
    Join Date
    Dec 2012
    Location
    LONDON
    Age
    44
    Posts
    14
    Rep Power
    0

    Re: daikin REYQ16M8W1B inverter compressor not running?

    much obliged m8

    ta

  11. #11
    Join Date
    May 2008
    Location
    dublin
    Posts
    80
    Rep Power
    16

    Re: daikin REYQ16M8W1B inverter compressor not running?

    Daikin app on the iPhone is pretty handy for faults etc ..

  12. #12
    Join Date
    Jul 2007
    Location
    ENGLAND
    Posts
    19
    Rep Power
    0

    Re: daikin REYQ16M8W1B inverter compressor not running?

    I have the manuals for these units in PDF format, Email me and I will send them over. If your unit is independent,ie not linked to any other condensing units then the only reason the inverter compressor is not running is because it has been programmed out, if the previous engineer has done this due to inverter comp failure, probably mechanically failed but still reads clear on winding and down to earth. This is the only way you will get D.O.L comps to run before the inverter compressor.