    Worcester Bosch Greensource 9.5kW



    Gents

    I had a call from a new customer with no heating and attended yesterday.

    It's the first time that I had my hands on one of these WB Greensource units and I traced the fault to the compressor soft start controller - a Carlo Gavazzi RSBS2325.

    It's difficult to work out what the alarm led means but it looked like a relay protection error. Thinking that it may be a duff compressor I meggered the windings but they were fine.

    Not being able to tell if it is a locked rotor fault without stating the machine, I'm left with little option but to replace the soft start first.

    Here's the rub....no stock in the UK and this particular model is for the German market where the units are made.

    Anyone have any experience on these WB systems?

    The nice guy at Carlo Gavazzi UK says that he can't recommend a replacement starter as the model I have ends with a 'S180' and he thinks that these were specially made for WB and the internal cut out limits may be different - he says WB must advise a replacement model that is suitable for their machine.

    In the meantime, the customers house is getting very cold.

    WB won't talk to me and won't supply spares and say I must go through their distributors. Parts Centre are struggling as well to identify a part...

    The full part number is RSBS2325A2V11C24S180 - 1phase compressor controller
    The compressor is a Mitsubishi AEH60VEH....3230w INPUT @ 50HZ



  2. #2
    Join Date
    Dec 2010
    Location
    Ireland
    Posts
    339
    Rep Power
    15

    Re: Worcester Bosch Greensource 9.5kW

    Quote Originally Posted by frank View Post
    Gents

    I had a call from a new customer with no heating and attended yesterday.

    It's the first time that I had my hands on one of these WB Greensource units and I traced the fault to the compressor soft start controller - a Carlo Gavazzi RSBS2325.

    It's difficult to work out what the alarm led means but it looked like a relay protection error. Thinking that it may be a duff compressor I meggered the windings but they were fine.

    Not being able to tell if it is a locked rotor fault without stating the machine, I'm left with little option but to replace the soft start first.

    Here's the rub....no stock in the UK and this particular model is for the German market where the units are made.

    Anyone have any experience on these WB systems?

    The nice guy at Carlo Gavazzi UK says that he can't recommend a replacement starter as the model I have ends with a 'S180' and he thinks that these were specially made for WB and the internal cut out limits may be different - he says WB must advise a replacement model that is suitable for their machine.

    In the meantime, the customers house is getting very cold.

    WB won't talk to me and won't supply spares and say I must go through their distributors. Parts Centre are struggling as well to identify a part...

    The full part number is RSBS2325A2V11C24S180 - 1phase compressor controller
    The compressor is a Mitsubishi AEH60VEH....3230w INPUT @ 50HZ
    Why not just run it without the softstart, from the draw it looks like it would require a 100 or 120uf capacitor.

  3. #3
    Join Date
    Dec 2010
    Location
    Ireland
    Posts
    339
    Rep Power
    15

    Re: Worcester Bosch Greensource 9.5kW

    Are you sure its a 3.2kw input. That would leave the COP at under 3.

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Worcester Bosch Greensource 9.5kW

    http://uk.farnell.com/schneider-elec...30%2B110030043 last resort if you dont want to bypass the soft start

  5. #5
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,471
    Rep Power
    41

    Re: Worcester Bosch Greensource 9.5kW

    They look the same as the ones used on Danfoss heat pumps, try HPI in Ireland, http://www.heatpumpsireland.com/
    Alternatively Fridge spares wholesale in ireland stock them, give Robbie a ring on 00353214317645

    As to being specifically programmed to Mitsubishi, for no heat i would fit this until the direct replacement can be sourced?

    al
    Mostly found in the southern part of this green and pleasant land.

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Worcester Bosch Greensource 9.5kW

    Thanks guys
    After speaking to a chap at emmerson I managed to get an alternative soft start from HRP
    Danfoss do one as well ...called a 1phase compressor soft starter
    As the house is out in the sticks on an 80amp supply, I didn't feel confident in bypassing the starter. LRA for the mitsi compressor is 121A

  7. #7
    Join Date
    Dec 2010
    Location
    Ireland
    Posts
    339
    Rep Power
    15

    Re: Worcester Bosch Greensource 9.5kW

    Quote Originally Posted by frank View Post
    Thanks guys
    After speaking to a chap at emmerson I managed to get an alternative soft start from HRP
    Danfoss do one as well ...called a 1phase compressor soft starter
    As the house is out in the sticks on an 80amp supply, I didn't feel confident in bypassing the starter. LRA for the mitsi compressor is 121A
    The Emmerson soft start are a nice unit and very reliable. Can't understand for the life of me why there would be a compressor of that size on a 9.5kw machine. We'd only have a compressor that size on a 19kw unit.

  8. #8
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Worcester Bosch Greensource 9.5kW

    Here's a picture of the compressor 3230W input @ 50hz

    Last edited by frank; 18-12-2012 at 11:50 PM.

  9. #9
    Join Date
    Dec 2010
    Location
    Ireland
    Posts
    339
    Rep Power
    15

    Re: Worcester Bosch Greensource 9.5kW

    Quote Originally Posted by frank View Post
    Here's a picture of the compressor 3230W input @ 50hz


    Wasn't doubting you frank. Just think its nuts

  10. #10
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Worcester Bosch Greensource 9.5kW

    Quote Originally Posted by Bigfreeze View Post
    Wasn't doubting you frank. Just think its nuts
    Didn't think you were Bigfreeze
    Just thought you might like to see one of my pictures

  11. #11
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,445
    Rep Power
    37

    Re: Worcester Bosch Greensource 9.5kW

    just to add I had a big heater battery with two CG solid state relay's one of which failed. CG UK stated 7 weeks for delivery so I wonder if they don't actually hold any stock at all?

    managed to get a different one next day for half the price which is working a-ok

  12. #12
    Join Date
    Dec 2010
    Location
    Ireland
    Posts
    339
    Rep Power
    15

    Re: Worcester Bosch Greensource 9.5kW

    Quote Originally Posted by frank View Post
    Didn't think you were Bigfreeze
    Just thought you might like to see one of my pictures
    And very pretty it is too Frank. Must have taken ages to get the angle and light just right

  13. #13
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Worcester Bosch Greensource 9.5kW

    Quote Originally Posted by Bigfreeze View Post
    And very pretty it is too Frank. Must have taken ages to get the angle and light just right
    Com'n on now....you are just trying to butter me up