    I changed old one with new controller but it can not work.
    Controller is for cooling chamber (cold room).
    Situation is next:
    -on the left side 3 leds blink all the time
    -I checked parameters ...it's OK
    -if I understand I must hold top button few second to see alarm message
    -massage is A42 ....but I don't have that alarm message in list ....so I don't know meanings
    Sep 2003
    ISRAEL
    72
    4,248
    Re: Electronic controller danfoss ekc 202 d
    Dec 2009
    Montenegro
    I all ready have this parameter list,but there are no parameter A45
    Jul 2001
    Sydney, Australia
    753
    Make sure parameters o02 and o37 are set to "off" to begin with (these are the digital input functions), then once you have it running if you need to use the digital inputs then program them in and test them one by one.
    ...and she said "give it to me you big fridgie"
    Dec 2009
    Montenegro
    I changed parameter r12 from 0 to 1.After that alarm A45 was disappeared and also LED,but I have new problem.
    Now regulator can not start compresor.
    I think that is necessary to change some more parameters.
    Question is which one???
    Dec 2009
    Montenegro
    I replace this danfoss regulator and put new LAE.
    Working very good.
    Jan 2006
    Norway
    1,035
    4
    31
    A45 is an alarm
    A45: Standby position (stopped refrigeration via r12 or DI input
    -Cheers-
    Tycho