    Electronic controller danfoss ekc 202 d



    I changed old one with new controller but it can not work.
    Controller is for cooling chamber (cold room).
    Situation is next:
    -on the left side 3 leds blink all the time
    -I checked parameters ...it's OK
    -if I understand I must hold top button few second to see alarm message
    -massage is A42 ....but I don't have that alarm message in list ....so I don't know meanings
    Attached Images Attached Images



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Electronic controller danfoss ekc 202 d


  3. #3
    Join Date
    Dec 2009
    Location
    Montenegro
    Age
    50
    Posts
    16
    Rep Power
    0

    Re: Electronic controller danfoss ekc 202 d

    I all ready have this parameter list,but there are no parameter A45
    ???
    Last edited by kopex; 14-12-2012 at 06:27 PM.

  4. #4
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25

    Re: Electronic controller danfoss ekc 202 d

    Make sure parameters o02 and o37 are set to "off" to begin with (these are the digital input functions), then once you have it running if you need to use the digital inputs then program them in and test them one by one.
    ...and she said "give it to me you big fridgie"

  5. #5
    Join Date
    Dec 2009
    Location
    Montenegro
    Age
    50
    Posts
    16
    Rep Power
    0

    Re: Electronic controller danfoss ekc 202 d

    I changed parameter r12 from 0 to 1.After that alarm A45 was disappeared and also LED,but I have new problem.
    Now regulator can not start compresor.
    I think that is necessary to change some more parameters.
    Question is which one???

  6. #6
    Join Date
    Dec 2009
    Location
    Montenegro
    Age
    50
    Posts
    16
    Rep Power
    0

    Re: Electronic controller danfoss ekc 202 d

    I replace this danfoss regulator and put new LAE.
    Working very good.

  7. #7
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,036
    Blog Entries
    4
    Rep Power
    31

    Re: Electronic controller danfoss ekc 202 d

    A45 is an alarm
    A45: Standby position (stopped refrigeration via r12 or DI input
    -Cheers-

    Tycho