    WTK plate heat exchanger as a condenser



    Anyone has expirence with WTK plate heat exchanger (P7-20)as a condenser
    Is hot gas from compressor should be connected to the top or bottom?
    thank you



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: WTK plate heat exchanger as a condenser

    Pipe connections depend on the model number reference, see here...
    http://www.wtk.it/en/prod_piastre_monocircuito.asp
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jan 2005
    Location
    POLAND
    Age
    50
    Posts
    18
    Rep Power
    0

    Re: WTK plate heat exchanger as a condenser

    Thanks Brian UK belive me but there is no information about it
    But with the plate heat exchanger came installation manual IMG_2040.jpg
    and it says from the bottom but I think its incorrect

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: WTK plate heat exchanger as a condenser

    Discharge allwyas on top so that the condensed liquid can flow down.