    Hey guys I'm new and I need some help. I am trying to find out the design evap/cond approach on a CVHF570 S#L08B00859. I also need to know if any press/temp/IGV can be calibrated. The customer has reduced loads to keep it out of surge. This is a design level 3N manufactured in 08. It has .025" wall internally enhanced tubes.
    Cond. Approach 7
    Evap approach 3-4
    Suction superheat 4-6 (Pipe skin temp no well)
    Discharge superheat 16
    IGV 50%
    RLA 100%
    Cond. diff P 7-8 psi should be 9
    Evap diff P 15 psi should be 7
    Cond delta T 13 which is design
    Evap Delta T is 6 design is 9
    I believe the tubes are fouled and it is low on refrigerant but the discharge superheat seems low. I cannot get any more water flow and have to wait until January for shutdown to inspect the tubes. At the same time to much chill water flow may be affecting the approach and suction superheat plus over working the condenser. If I new the design approach it would help.



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: CVHF help

    The condenser TD (K) or approach is the design saturated condensing temperature less the highest potential air on temperature. Wet bulb temperatures also influence evap condenser capacity, high wet bulb reduces capacity.

    Have you checked system for non-condensibles, which will accumulate in evap/condenser, reduce performance and total heat of rejection.
    Last edited by Magoo; 11-12-2012 at 03:59 AM. Reason: spelling

  3. #3
    Join Date
    Dec 2012
    Location
    Louisiana
    Age
    41
    Posts
    4
    Rep Power
    0

    Re: CVHF help

    The drain leg temp equals sat temp for given pressure. I can't get my hands on the design refrig temps for evap/cond. I do have the design water temps

  4. #4
    Join Date
    Feb 2008
    Location
    sydney
    Age
    52
    Posts
    32
    Rep Power
    0

    Re: CVHF help

    pressures and temperatures

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •