Results 1 to 8 of 8
    Apr 2012
    Iraq
    29
    610
    10
    how to charge 2 to split ac unit in heating mode
    hi every one
    how to charge 2 ton split ac unit in heating mode
    it is commonly when charging ac
    u must charge it while running it in cooling mode
    but if i want to charge it while its running in heating mode
    what i must do
    must i disconnect the reverse valve from pcb
    or connect the charging hose to the discharge connection valve in the split instead of suction connection valve
    best regards
    Apr 2008
    Southampton, England
    43
    895
    27
    Re: how to charge 2 to split ac unit in heating mode
    Unless you can get to a suction port (between compressor and 4WV) then you need to charge in cooling as the service port is the suction pipe in this mode otherwise in heating it's discharge gas.
    If you select heat then perhaps get 4WV to stay in cooling should work, but after flaffing around might just as well select cooling anyhow - might have to heat air on probe or select test run.
    Apr 2008
    43
    895
    27
    Quote Originally Posted by kefah View Post
    best regards
    Are you thinking of the service port on the small pipe? In heating this is high pressure liquid refrigerant so you'd be unable to use this port to charge.
    Apr 2008
    West Yorkshire
    36
    10
    Does the compressor pull from the accumulator in heating?? Just a random question.
    Apr 2008
    43
    895
    27
    Yes.
    Search for a piping diagram of a heat pump and follow the system in heating or cooling. Should make a bit more sense to begin with than looking at the pipes on a unit,
    Apr 2008
    West Yorkshire
    36
    10
    So the compressor pulls from the accumulator, which tells me if there is a service port inbetween the condenser and accumulator, gas should be able to be dumped in there as this should be low pressure vapour. But there probably isnt going to a service port in between the condenser and accumulator.
    Apr 2008
    43
    895
    27
    Yep, that's right.
    Service ports a bit thin on the ground on splits. Some might have a port inside on a discharge pipe perhaps (used for charging at the factory I think) other than that it's the one or two on the service valves.
    Apr 2012
    Iraq
    29
    610
    10
    thank u all
    the best way to charge in winter
    i s turn ing on split in heating mode then disconnecting the 4 way valve
    and chjarging the split through suction valve ( the largest pipe valve )
    thank u for help
    please close the thread