    over condensing..



    Hi all,

    Any idea for ***** R22 system over condensing? over sizing for watercool condenser?
    and what is the right pressure and temperature for the system?

    thanks.



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: over condensing..

    I would think 30C would be a good minimum condensing temperature, though it depends on you system, expect a balanced port txv or an eev would cope better with low condensing temperatures.

    Heres a vid i took of an air cooled system in winter time,

    http://www.youtube.com/watch?v=l28FPhN3yY4
    Mostly found in Oxfordshire, UK :)

  3. #3
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: over condensing..

    i think water temp rise of between 5 or 10 degc condensing water temp

  4. #4
    Join Date
    May 2008
    Location
    malaysia
    Age
    40
    Posts
    82
    Rep Power
    16

    Re: over condensing..

    ok, thanks for ur reply.

  5. #5
    Join Date
    Oct 2010
    Location
    Australia
    Posts
    88
    Rep Power
    15

    Re: over condensing..

    I recently replaced the air cooled condenser on my heat pump with a *big* bphx. It used to condense at abut 55-60C and now condenses at ~25C with ~1.5K subcooling. I had already replaced the fixed orifice with an EEV, so I don't know what the drop in pressure would have done to the original metering device. I can say that the capacity of the system has increased significantly.

    I suspect as long as your metering device can cope with the reduced pressure differential, the lower you can condense, the better. My ground water loop is at about 20C so I can't really get it much lower than I am right now.

    I'm waiting on a flow meter to arrive so I can properly quantify the heat being rejected into the water.

    Overall, and taking into account replacing a 30W condenser fan with a 150W water pump, my net power consumption has dropped over 750W, but I'm also moving a *lot* more heat. My supply air temp has dropped from 17C to 13C on average.

  6. #6
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: over condensing..

    The ideal SDT for R22 is between +32 and +35 'C to maintain system balance. Use a water regulatig valve pressure controlled on outlet water on water cooled condenser, on larger systems have a minimum flow bypass to maintain flow to stop water pump dead heading with no flow

  7. #7
    Join Date
    Oct 2010
    Location
    Australia
    Posts
    88
    Rep Power
    15

    Re: over condensing..

    Quote Originally Posted by Magoo View Post
    The ideal SDT for R22 is between +32 and +35 'C to maintain system balance.
    Pardon my ignorance, but isn't that a bit of a handwaving generality? I'd have thought the ideal would be what the system was designed for as a minimum rather than some arbitrary value.