    Exclamation Delta T for chiller, AHU & district cooling systems
    Hi all..
    Can anyone please explain me the concept of delta T & what delta T shall be considered for Chillers, Ahu & district cooling systems?
    Regards
  2. #2
    Join Date
    May 2011
    Location
    India
    Age
    38
    Posts
    106
    Rep Power
    14
    Re: Delta T for chiller, AHU & district cooling systems
    delta T is the temp difference between the chilled water inlet and outlet.
    The pipe size depends on this value.
    Generally this value is 12, for hich the water requirement is 2.4GPM/TR.
    And, for delta T 10, the water requirement is 2GPM/TR..
    What value for delta T to choose entirely depends on the clients budget. . I think, since even I have not though about it. In mu concept, at 10 delta T, there would be considerble savings in pipe qty.