    Exclamation Delta T for chiller, AHU & district cooling systems



    Hi all..
    Can anyone please explain me the concept of delta T & what delta T shall be considered for Chillers, Ahu & district cooling systems?

    Regards



  2. #2
    Join Date
    May 2011
    Location
    India
    Age
    38
    Posts
    106
    Rep Power
    13

    Re: Delta T for chiller, AHU & district cooling systems

    delta T is the temp difference between the chilled water inlet and outlet.
    The pipe size depends on this value.
    Generally this value is 12, for hich the water requirement is 2.4GPM/TR.
    And, for delta T 10, the water requirement is 2GPM/TR..

    What value for delta T to choose entirely depends on the clients budget. . I think, since even I have not though about it. In mu concept, at 10 delta T, there would be considerble savings in pipe qty.
    Last edited by nevinjohn; 14-03-2013 at 08:28 AM.