    Hi. So we are trying to make an air dryer design for our thesis project. I wanted to ask how to choose a liquid receiver for our design. and the amount of refrigerant needed. Our objective was to cool the air from 25 degree celsius to 3 degrees.
    Thanks



  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: Refrigerated Air Dryer

    .

    Don't start with the receiver.

    Start by calculating the load on the evaporator first,
    then you will be able to calculate the compressor, condenser
    and the mass flow rates of the refrigerant.

    That will tell you how much refrigerant you need and then you
    can pick the size of the receiver.

    To be honest though the receiver size is the least important component
    on the whole system. the receiver needs to be large enough to hold
    the entire refrigerant charge with a little bit of space left over for expansion.

    Normal requirements are for an oversize of 10%.

    Regards

    Rob

    .

  3. #3
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Refrigerated Air Dryer

    Liquid receivers are quickly disappearing from modern refrigeration circuits, especially for those applications that have fixed and stable working conditions.
    So, my answer here would be: "no liquid receiver needed".

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Refrigerated Air Dryer

    Don't forget the amount of air you want to cool.

  5. #5
    Join Date
    Dec 2012
    Location
    Philippines
    Age
    33
    Posts
    2
    Rep Power
    0

    Re: Refrigerated Air Dryer

    Thanks..now I know..really helps.. So our evaporator design is to wrap an air tank with copper coils..my problem is how to determine the surface are for heat transfer since most of the books focus on a direct coil contact..thanks again.

  6. #6
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Refrigerated Air Dryer

    It will not work,
    You need heat exchanger of some kind.
    You can not re invent the wheel. get an old scrap refrigerated air drier, take it apart and learn how doe's it work.

  7. #7
    Join Date
    May 2011
    Location
    India
    Age
    38
    Posts
    106
    Rep Power
    13

    Re: Refrigerated Air Dryer

    Quote Originally Posted by NoNickName View Post
    Liquid receivers are quickly disappearing from modern refrigeration circuits, especially for those applications that have fixed and stable working conditions.
    So, my answer here would be: "no liquid receiver needed".
    So, under normal circumstances a domestic split unit has refrigerent in the entire pipe system I suppose? What is the state of refrigerent, liquid or gas (when the unit is turned off). I assume the entire system should be vapour as it absorves heat from the room, and from outside (for the condensing unit)?

    Will there be a liqid flow back to the compressor once the unit (compressor) turns off when the desired temperature is reached? Is there any preventive circuit for this? - I am reffering to the discharge line.