    Differential pressure - 2 Way valve



    Could I measure the differential pressure through the valve (DPv ) by: (DPv ) = Ps – DPcoil - Pr , like showed on the sketch below? Is it correct to measure this way? Or measuring by CBI through the STAD is it possible to measure the DPv ? What’s the right procedure to measure the valve DPv?




    If the DH could be very higher is it necessary to install a modulating relief valve e.g BPV (TA) to reduce the differential pressure by a constant value?




    Thanks in advance.



  2. #2
    Join Date
    Nov 2007
    Location
    Brazil
    Age
    42
    Posts
    31
    Rep Power
    0

    Re: Differential pressure - 2 Way valve

    HSL.png

    Here is the sketch.

  3. #3
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: Differential pressure - 2 Way valve

    as the pressure drop will prob be low the corect way is through the stad as this can be converted to flow using the corect chart for the valve

  4. #4
    Join Date
    Nov 2007
    Location
    Brazil
    Age
    42
    Posts
    31
    Rep Power
    0

    Re: Differential pressure - 2 Way valve

    Martin, First , thank you for your answer,
    But the readings through the STAD , Wouldn't be only the differential pressure across the STAD and not the differential pressure through the control valve (V)?


    Thanks