    Could I measure the differential pressure through the valve (DPv ) by: (DPv ) = Ps – DPcoil - Pr , like showed on the sketch below? Is it correct to measure this way? Or measuring by CBI through the STAD is it possible to measure the DPv ? What’s the right procedure to measure the valve DPv?
    If the DH could be very higher is it necessary to install a modulating relief valve e.g BPV (TA) to reduce the differential pressure by a constant value?
    Thanks in advance.
    Nov 2007
    Brazil
    36
    21
    Re: Differential pressure - 2 Way valve
    Here is the sketch.
    Feb 2008
    384
    12
    as the pressure drop will prob be low the corect way is through the stad as this can be converted to flow using the corect chart for the valve
    Nov 2007
    Brazil
    36
    21
    Martin, First , thank you for your answer,
    But the readings through the STAD , Wouldn't be only the differential pressure across the STAD and not the differential pressure through the control valve (V)?