    tecumseh single phase compressor wiring



    hi guys im working on a small 3kw water chiller and the compressor is being changed. The original comp had only 1 run capacitor and thermal oload.But the new comp has start cap and run cap and a relay supplied with it. On the comp it has everthing same details but on the box it came in says CSR.Can it be wired same as old one with only 1run capacitor or do i need to wire it in with full set of electrics it came in with.Thankyou



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: tecumseh single phase compressor wiring

    wire as a csr comp, just l,n,e to the box, make sure the box is mounted securely and upright, you will wire a pressure switch accross L and 1- if no press switch the fit a link,also hook ur cond fan up to 1,n e job done

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: tecumseh single phase compressor wiring


  4. #4
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: tecumseh single phase compressor wiring

    Thankyou guys. I couldnt understand why 1 comp runs on run cap connected to the start winding and new machine comed in with different electrics set up

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: tecumseh single phase compressor wiring

    1 cap compressor- psc type high start torque, you'll know for next time

  6. #6
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: tecumseh single phase compressor wiring

    Thankyou for info friend

  7. #7
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: tecumseh single phase compressor wiring

    Quote Originally Posted by GHAZ View Post
    hi guys im working on a small 3kw water chiller and the compressor is being changed. The original comp had only 1 run capacitor and thermal oload.But the new comp has start cap and run cap and a relay supplied with it. On the comp it has everthing same details but on the box it came in says CSR.Can it be wired same as old one with only 1run capacitor or do i need to wire it in with full set of electrics it came in with.Thankyou
    Just out of interest are you planning on using the old electrics on the
    new compressor? It always makes sense to replace all the electrics
    with the new ones supplied, because there may be something wrong
    with the old electrics!

    Regards

    Rob

    .

  8. #8
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: tecumseh single phase compressor wiring

    Hi rob i changed all new electrics