    Night setbacks and timers



    I have a client who wants a Fujitsu split. She would like to take advantage of time of use rates and night setback but the one I have can't do either. Is there one that can?

    The ones available here are of this series ...24RLXFW

    I should have said that there would have to be more than 2 changes in program daily.
    Last edited by MikeHolm; 29-11-2012 at 01:27 AM.



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Night setbacks and timers

    ASU24RLF
    INDICATOR PCB ASSEMBLY
    K05CY-0902HSE-D0 is an optional pcb for the outdoor unit with input/output connections. a standard digi time clock will give a few switched schedules but then for your night set back you would have to wire a volt free room stat across the sitch contacts on the time clock so even in off mode, setback temp can be maintained. i'll email u install and service manuals- 2 separate e mails, no diet pills emails

  3. #3
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,492
    Rep Power
    24

    Re: Night setbacks and timers

    Cool, got the manuals. I have to see if Sanyo comes in at an equivalent cost.

  4. #4
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,045
    Rep Power
    35

    Re: Night setbacks and timers

    If you get the wired remote you can use the timer on that which also has a setback timer.

    The indoor PCB has connections for an external input. When the outside pins of CN14 are connected the unit will turn on at the settings it was last in.
    Health and safety first..........unless I'm in a hurry.

  5. #5
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,492
    Rep Power
    24

    Re: Night setbacks and timers

    Quote Originally Posted by Tayters View Post
    If you get the wired remote you can use the timer on that which also has a setback timer.

    The indoor PCB has connections for an external input. When the outside pins of CN14 are connected the unit will turn on at the settings it was last in.
    Fujitsu or sanyo?

  6. #6
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,045
    Rep Power
    35

    Re: Night setbacks and timers

    Hi Mike,

    That's the Fujitsu one assuming it's the ASU24RLF / AOU24RLXFW.