    Hi ,

    What's the purpose of the internal drain trap on dowflow self contained units installed on raised floor ?
    is it to avoid outside air flow to the internal unit through the drain line due the diferencial pressure (External - internal)?

    Thanks a lot.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Internal Drain trap

    A drain trap will ensure that air pressure does not affect the water flow through the drain.

    For example, if the drain should be on the inlet side of the fan then it will operate under a negative pressure and no water will flow out through the pipe.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Nov 2007
    Location
    Brazil
    Age
    42
    Posts
    31
    Rep Power
    0

    Re: Internal Drain trap

    Ok. So , if the drain shoud be on the outlet side of the fan (positive pressure), then the drain trap will not have effect, correct? In this case could I eliminate the drain trap?

    Thanks.

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Internal Drain trap

    I would use a trap on both sides of the fan.

    It stops air leakage from the unit, it will also stop any air noise that may be generated by the leaking air.

    It will stop any foul odours flowing back into the unit and reduce the risk of mould spores getting into the unit/ductwork.

    http://www.cfm.va.gov/til/sDetail/Di...D232113-08.pdf
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Internal Drain trap

    It prevent moisture migration as well.