    Unhappy Water into the system!!! help me



    hello everyone!
    i have a industrial REFRIGERATION system, it use R407c, condenser was cooled by water. AND trouble is my condenser was leaked, water into the system
    how to take it out thoroughly???
    thanks you in advance



  2. #2
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Water into the system!!! help me

    hi k,
    you need a fan assisted gas heater to blow on to the system and onto the ofn bottles which you need to blow through the system once you have found the leak , if there is space enough to split the
    fridge system then do so especially the compressor, drain the oil( and water )
    new dryes, vac out, gas up , best of luck= sedgy
    Last edited by sedgy; 24-11-2012 at 08:38 PM.

  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Water into the system!!! help me

    Any and all of the oil in the system is now acidic, drain as much of it as possible.

    Flush the system with as much OFN as you can get your hands on.

    Several deep vacuums, each broken by OFN.

    New driers, make sure there are valves before and after the drier(s).

    Triple vacc and recommission.

    Run for a day or so then change the drier. Repeat this step as necessary.
    After a week or so replace the oil.


  4. #4
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,554
    Rep Power
    26

    Re: Water into the system!!! help me

    I going to get my arse kicked here.

    Isolate the compressor, flush with a a cleaning agent.
    Now the system, fit valves at low points!
    Flush the system with very hot water (80C) plus "Yes hot water"
    When clean of shyte, drain hot water, and blow through the system with hot air. ( I actually draw through a system with a vaccum cleaner (a air heater on the inlet)).
    This will remove all the crude, the heat will remove most free water.
    Now, purge OFN warm if possible.
    Vacuum the system, own to 200 micron or below.
    Keep heat on the system if possible.
    This is a quicker and better, than trying to clean a system, with OFN only.

  5. #5
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Water into the system!!! help me

    Demineralised water "Mad"??
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  6. #6
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,554
    Rep Power
    26

    Re: Water into the system!!! help me

    Quote Originally Posted by mikeref View Post
    Demineralised water "Mad"??
    In a perfect world, but just clean filtered tap water is OK,

    The water that is already in the system is likely to have more crap in it.

    Hot water will loosen any oil (which will be contaminated) that within the system, hot water will flow more easily out of the system (so already less free water), when air is applied.
    Because the internals are hot the any free water will evaporate very easily.
    Your filters (which should always be fitted after this type of fault) will pick up any deposited TDS (total dissolved solids) which will be minimal.

  7. #7
    Join Date
    Oct 2010
    Location
    thu duc
    Age
    34
    Posts
    28
    Rep Power
    0

    Re: Water into the system!!! help me

    "all of the oil in the system is now acidic" why is that?
    thanks for your help!

  8. #8
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Water into the system!!! help me

    Quote Originally Posted by khongminhhason View Post
    "all of the oil in the system is now acidic" why is that?
    thanks for your help!
    Because of the water.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  9. #9
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Water into the system!!! help me

    Quote Originally Posted by khongminhhason View Post
    "all of the oil in the system is now acidic" why is that?
    thanks for your help!
    Water can break down the chemicals that are the ingreadients of the oil, kind of undoes the manufactuing process.

    Also the water will have likely brought in suspended dirt and grit and left it behind.

    Depending on the system and how much water got in, it may be better (cheaper in long term/more reliable) to scrap the system and replace with new.
    Mostly found in Oxfordshire, UK :)