    Liebert HP



    Hi,
    Problem with Liebert CCU with water cooled condenser and free-cooling .
    On first start, compressor go on Hi pressure(25bar.). After reset alarm, compressor starts and work without problem. I can switch on/off compressor several times it will work without problem, if compressor is off longer, on next start compressor will go on HP alarm.
    Any suggestions, is it problem in head pressure valves or...



  2. #2
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Liebert HP

    Are your water pumps going off too??
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  3. #3
    Join Date
    Dec 2007
    Location
    Macedonia
    Age
    48
    Posts
    42
    Rep Power
    0

    Re: Liebert HP

    No,
    water pump is always on,
    water pressure - ok,
    water valve -open
    amount of refrigerant-ok
    ref.valve-open
    only first start of compressor is problem, after that unit can work all day without problem.

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Liebert HP

    expansion valve may be causing issues as it can take a few minutes to stabilize

  5. #5
    Join Date
    Dec 2007
    Location
    Macedonia
    Age
    48
    Posts
    42
    Rep Power
    0

    Re: Liebert HP

    i have head pressure valve after compressor on hi pressure side, his function is to open bypass from hi to low pressure side to, balance hi pressure on compressor start.
    correct me if i'm wrong.

  6. #6
    Join Date
    Dec 2007
    Location
    Macedonia
    Age
    48
    Posts
    42
    Rep Power
    0

    Re: Liebert HP

    any suggestions, how can i solve this problem, please.

  7. #7
    Join Date
    Mar 2008
    Location
    Ireland
    Age
    39
    Posts
    9
    Rep Power
    0

    Re: Liebert HP

    Quote Originally Posted by slavex View Post
    any suggestions, how can i solve this problem, please.
    Is there a ball valve and actuator on the water line?

  8. #8
    Join Date
    Dec 2007
    Location
    Macedonia
    Age
    48
    Posts
    42
    Rep Power
    0

    Re: Liebert HP

    yes there is, but i disable free cooling so valve is closed and all water flow goes true condenser

  9. #9
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Liebert HP

    is the strainer on water circuit clear?

  10. #10
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Liebert HP

    liebert units have a head pressure control that regulate and if req inject into liq receiver- try adjusting it to allow more into the condenser

  11. #11
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: Liebert HP

    Where you take water? Drycoolers? What temperature outdoor?

  12. #12
    Join Date
    Dec 2007
    Location
    Macedonia
    Age
    48
    Posts
    42
    Rep Power
    0

    Re: Liebert HP

    Quote Originally Posted by install monkey View Post
    is the strainer on water circuit clear?
    yes strainer is clear, only first start is problem after reset compressors work perfectly.

  13. #13
    Join Date
    Dec 2007
    Location
    Macedonia
    Age
    48
    Posts
    42
    Rep Power
    0

    Re: Liebert HP

    Quote Originally Posted by install monkey View Post
    liebert units have a head pressure control that regulate and if req inject into liq receiver- try adjusting it to allow more into the condenser
    yes there is head pressure valve LAC 5-with fixed pressure of 180 psig. i think it is can not be regulated.

  14. #14
    Join Date
    Dec 2007
    Location
    Macedonia
    Age
    48
    Posts
    42
    Rep Power
    0

    Re: Liebert HP

    Quote Originally Posted by RusBuka View Post
    Where you take water? Drycoolers? What temperature outdoor?
    in drycooler, outdoor temp. 10

  15. #15
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Liebert HP

    whats the hp switch set to trip at and does it trip at the stated pressure?

  16. #16
    Join Date
    Dec 2007
    Location
    Macedonia
    Age
    48
    Posts
    42
    Rep Power
    0

    Re: Liebert HP

    hp switch is set on 26 bar-i caught that pressure several times, so alarm is real



    sorry if i don't understand your question properly

  17. #17
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: Liebert HP

    have you check valve or solenoid between discharge pipe and water condenser? And have you any valve after condenser?

  18. #18
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Liebert HP

    what make , model is the head pressure control?- usually they have an adjusting screw, can it be swapped to prove it works?
    Quote Originally Posted by slavex View Post
    yes there is head pressure valve LAC 5-with fixed pressure of 180 psig. i think it is can not be regulated.

  19. #19
    Join Date
    Dec 2007
    Location
    Macedonia
    Age
    48
    Posts
    42
    Rep Power
    0

    Re: Liebert HP

    there is cpce valve on discharge line nothing else.
    and after condenser- lac-5, one way valve liq.receiver, filter,solenoid, exp.valve. I switch solenoid on always to eliminate it.

  20. #20
    Join Date
    Dec 2007
    Location
    Macedonia
    Age
    48
    Posts
    42
    Rep Power
    0

    Re: Liebert HP

    Quote Originally Posted by install monkey View Post
    what make , model is the head pressure control?- usually they have an adjusting screw, can it be swapped to prove it works?
    http://www.legacychillers.com/cms_da...oodedvalve.pdf

  21. #21
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Liebert HP

    is there another unit on site you can compare pressures,temps,running current? when the system stops when at setpoint liquid isn't flooding the evap so upon startup it trips?

  22. #22
    Join Date
    Dec 2007
    Location
    Macedonia
    Age
    48
    Posts
    42
    Rep Power
    0

    Re: Liebert HP

    yes i have another unit, same model,pipe length, water pump, pressure ...it is working without problem.

    if compressor stops at setpoint and after short brake start up again it will work without problem, if there is longer brake next start is always with HP.

  23. #23
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Liebert HP

    is there any settings on the controller or a delay timer that ignores the pressure switches on start up - may req increasing

  24. #24
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: Liebert HP

    how long it takes from start to crash, where there is a high pressure? something is blocking discharge at the first start.

  25. #25
    Join Date
    Dec 2007
    Location
    Macedonia
    Age
    48
    Posts
    42
    Rep Power
    0

    Re: Liebert HP

    Quote Originally Posted by install monkey View Post
    is there any settings on the controller or a delay timer that ignores the pressure switches on start up - may req increasing
    pressure switch on 26 bar cut off signal and i have to restart switch manually, i thought that i can put new switch set on 28 bar, but is big risk because i have safety valve on 30 bar.