23-11-2012, 01:47 PM #1
Liebert HP
Hi,
Problem with Liebert CCU with water cooled condenser and free-cooling .
On first start, compressor go on Hi pressure(25bar.). After reset alarm, compressor starts and work without problem. I can switch on/off compressor several times it will work without problem, if compressor is off longer, on next start compressor will go on HP alarm.
Any suggestions, is it problem in head pressure valves or...
-
23-11-2012, 09:26 PM #2
Re: Liebert HP
Are your water pumps going off too??
Cheers
StuTool's ? check ! Condom's ? check !
If you can't fix it , f*ck it !!!
-
23-11-2012, 10:16 PM #3
Re: Liebert HP
No,
water pump is always on,
water pressure - ok,
water valve -open
amount of refrigerant-ok
ref.valve-open
only first start of compressor is problem, after that unit can work all day without problem.
-
23-11-2012, 10:40 PM #4
Re: Liebert HP
expansion valve may be causing issues as it can take a few minutes to stabilize
-
23-11-2012, 11:10 PM #5
Re: Liebert HP
i have head pressure valve after compressor on hi pressure side, his function is to open bypass from hi to low pressure side to, balance hi pressure on compressor start.
correct me if i'm wrong.
-
07-12-2012, 07:55 AM #6
Re: Liebert HP
any suggestions, how can i solve this problem, please.
-
07-12-2012, 08:08 AM #7
-
07-12-2012, 08:21 AM #8
Re: Liebert HP
yes there is, but i disable free cooling so valve is closed and all water flow goes true condenser
-
07-12-2012, 06:15 PM #9
Re: Liebert HP
is the strainer on water circuit clear?
-
07-12-2012, 06:22 PM #10
Re: Liebert HP
liebert units have a head pressure control that regulate and if req inject into liq receiver- try adjusting it to allow more into the condenser
-
07-12-2012, 07:52 PM #11
Re: Liebert HP
Where you take water? Drycoolers? What temperature outdoor?
-
08-12-2012, 09:59 PM #12
-
08-12-2012, 10:35 PM #13
-
08-12-2012, 10:38 PM #14
-
08-12-2012, 10:46 PM #15
Re: Liebert HP
whats the hp switch set to trip at and does it trip at the stated pressure?
-
08-12-2012, 11:03 PM #16
Re: Liebert HP
hp switch is set on 26 bar-i caught that pressure several times, so alarm is real
sorry if i don't understand your question properly
-
08-12-2012, 11:16 PM #17
Re: Liebert HP
have you check valve or solenoid between discharge pipe and water condenser? And have you any valve after condenser?
-
08-12-2012, 11:18 PM #18
-
08-12-2012, 11:31 PM #19
Re: Liebert HP
there is cpce valve on discharge line nothing else.
and after condenser- lac-5, one way valve liq.receiver, filter,solenoid, exp.valve. I switch solenoid on always to eliminate it.
-
08-12-2012, 11:35 PM #20
Re: Liebert HP
-
08-12-2012, 11:39 PM #21
Re: Liebert HP
is there another unit on site you can compare pressures,temps,running current? when the system stops when at setpoint liquid isn't flooding the evap so upon startup it trips?
-
09-12-2012, 12:03 AM #22
Re: Liebert HP
yes i have another unit, same model,pipe length, water pump, pressure ...it is working without problem.
if compressor stops at setpoint and after short brake start up again it will work without problem, if there is longer brake next start is always with HP.
-
09-12-2012, 08:14 AM #23
Re: Liebert HP
is there any settings on the controller or a delay timer that ignores the pressure switches on start up - may req increasing
-
09-12-2012, 11:24 AM #24
Re: Liebert HP
how long it takes from start to crash, where there is a high pressure? something is blocking discharge at the first start.
-
09-12-2012, 03:38 PM #25