    Can i by-pass a relay on the common wire to the compressor ?



    Hi all,

    I was wondering if i can by-pass the wire going in to the little black relay and put it to the common terminal on the compressor just to see if the compressor runs and gets the customer going until i return with a new one, or is this to harmfull to the compressor?

    Replies would be appreciated....thanks



  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: Can i by-pass a relay on the common wire to the compressor ?

    .

    What you are suggesting in principle is acceptable and done quite regularly.

    But and it is a big but.. But you need to confirm the relay is faulty and not some
    other component. You also need to know what controls the relay and what
    the effect of by-passing it will have.

    If every thing is ok and the relay has simply failed then by-passing it would
    prove you to be correct, but remember the relay might be taking the load off
    the starting circuit. If you by pass the relay the load (electrical) will be
    on the control circuit and it might not be rated for it.

    Do it to test and prove your point but be very certain that the control circuit
    is designed for the starting current of the compressor. If you don't you
    will burn out some more pieces of equipment and will be worse off.

    Regards

    Rob

    .

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Can i by-pass a relay on the common wire to the compressor ?

    Why not just dead test the compressor?

  4. #4
    Join Date
    May 2007
    Location
    Northants
    Posts
    292
    Rep Power
    17

    Re: Can i by-pass a relay on the common wire to the compressor ?

    How do you dead test it??

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Can i by-pass a relay on the common wire to the compressor ?

    Dead test..i.e. no power applied.

    Megger the windings and measure the winding resistances

  6. #6
    Join Date
    Jul 2012
    Location
    united kingdom
    Age
    45
    Posts
    3
    Rep Power
    0

    Re: Can i by-pass a relay on the common wire to the compressor ?

    Quote Originally Posted by Rob White View Post
    .

    What you are suggesting in principle is acceptable and done quite regularly.

    But and it is a big but.. But you need to confirm the relay is faulty and not some
    other component. You also need to know what controls the relay and what
    the effect of by-passing it will have.

    If every thing is ok and the relay has simply failed then by-passing it would
    prove you to be correct, but remember the relay might be taking the load off
    the starting circuit. If you by pass the relay the load (electrical) will be
    on the control circuit and it might not be rated for it.

    Do it to test and prove your point but be very certain that the control circuit
    is designed for the starting current of the compressor. If you don't you
    will burn out some more pieces of equipment and will be worse off.

    Regards

    Rob

    .
    Thanks Rob, i by-passed it for half a day until i went back and got a new relay. Jobs a good one..

  7. #7
    Join Date
    Jul 2012
    Location
    united kingdom
    Age
    45
    Posts
    3
    Rep Power
    0

    Re: Can i by-pass a relay on the common wire to the compressor ?

    Thanks for the help Guys...
    Frank, cheers for that. I did do a resistance test and mechanically test which it was ok. I was just concerned in buggering it up by-passing the relay but the customer wanted it running there and then.

    cheers guys

  8. #8
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: Can i by-pass a relay on the common wire to the compressor ?

    .

    Glad it all worked out and thanks for getting back and
    letting us know the end result.....

    Regards

    Rob

    .