    r22 city multi problem



    Hello chaps just wondering if anyones cams across this problem before.
    I had a service call on the old r22 city multi today, 2 units in the chief executives office not heating.Anyway found the r/c set wrong ran on 24 heating worked fine. Decided to check all other units on heating, found 2 out of 6 wouldnt heat at all yet they will cool staifactory.Im sure the system is ok for gas because the pressures are norm and the furthest units are performing.is it worth swapping the solenoids for heating in the bc box with the cooling ones.Even tried re calibrting all the indoor exp valves.



  2. #2
    Join Date
    Dec 2005
    Location
    South East England
    Age
    56
    Posts
    155
    Rep Power
    19

    Re: r22 city multi problem

    may be worth checking the gas charge have heared of this problem before from another engineer they had exactly the same symptoms running fine in cooling but not in heating and it turned out to be short of gas , not sure why this occurs may be worth a check though

    hope this helps
    Noah had to leave the dinosaurs behind as they would've sunk the boat.

  3. #3
    Join Date
    Feb 2004
    Location
    Australia
    Posts
    286
    Rep Power
    21

    Re: r22 city multi problem

    Suction and discharge pressures won't tell you that much on a VRF. Take the front cover of the outdoor, and on the bottom right unscrew the metal cover, check for a fault code if there is one. Check EEVs for units and make sure the motors are opening them properly. If you think there is a refrigerant problem, then you will have to weigh it out to decide if the problem lies there.
    a problem shared is a problem halved

  4. #4
    Join Date
    Apr 2005
    Location
    manchester
    Age
    44
    Posts
    23
    Rep Power
    0

    Re: r22 city multi problem

    Hi there chaps, just to let you know i sorted the problem.it was a fulty coil (solenoid b) swapped it with one on a port not bieng used.
    The model was pury-250yma b.
    Thanx for your ideas anyway guys

Similar Threads

  1. Need input on City Multi
    By TDfromNY in forum Air Conditioning
    Replies: 4
    Last Post: 09-06-2006, 03:31 AM
  2. mitsi city multi r407c
    By mr slim in forum Air Conditioning
    Replies: 6
    Last Post: 06-03-2006, 10:54 PM
  3. Mitsi City Multi Compressor Death
    By aeb200 in forum Air Conditioning
    Replies: 4
    Last Post: 16-11-2005, 09:10 AM
  4. Mitsubishi city multi
    By techni in forum Air Conditioning
    Replies: 2
    Last Post: 04-07-2005, 05:37 PM
  5. city multi
    By techni in forum Air Conditioning
    Replies: 1
    Last Post: 30-06-2002, 11:02 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •