    Nov 2012
    Australia
    Need help senor reading chart
    hi everyone just need help need a chart reading with temp to ohms to test outdoor coil sensors and indoor
    Aug 2007
    Sydney
    1,083
    23
    Re: Need help senor reading chart
    Hi Jimmy
    http://www.datasheetarchive.com/temp...datasheet.html should help point you in the right direction. Most sensors used are Thermistors NTC and usually 10k but can come in like 2k 5k 20k 100k etc. If you measure your sensor at around 25degC you should get an idea of how many k it is.
    Most as suppliers of controls suppliers will charge from $25 to $250 for a sensor which you can buy from jaycar electronics for less than $5.
    Feb 2008
    505
    21
    Values for various popular resistance thermometers
    Temperature
    in °C
    Pt100
    in
    Ω
    Pt1000
    in Ω
    PTC
    in Ω
    NTC
    in Ω
    NTC
    in Ω
    NTC
    in Ω
    NTC
    in Ω
    NTC
    in Ω
    Typ: 404 Typ: 501 Typ: 201 Typ: 101 Typ: 102 Typ: 103 Typ: 104 Typ: 105
    −50 80.31 803.1 1032
    −45 82.29 822.9 1084
    −40 84.27 842.7 1135 50475
    −35 86.25 862.5 1191 36405
    −30 88.22 882.2 1246 26550
    −25 90.19 901.9 1306 26083 19560
    −20 92.16 921.6 1366 19414 14560
    −15 94.12 941.2 1430 14596 10943
    −10 96.09 960.9 1493 11066 8299
    −5 98.04 980.4 1561 31389 8466
    0 100.00 1000.0 1628 23868 6536
    5 101.95 1019.5 1700 18299 5078
    10 103.90 1039.0 1771 14130 3986
    15 105.85 1058.5 1847 10998
    20 107.79 1077.9 1922 8618
    25 109.73 1097.3 2000 6800 15000
    30 111.67 1116.7 2080 5401 11933
    35 113.61 1136.1 2162 4317 9522
    40 115.54 1155.4 2244 3471 7657
    45 117.47 1174.7 2330 6194
    50 119.40 1194.0 2415 5039
    55 121.32 1213.2 2505 4299 27475
    60 123.24 1232.4 2595 3756 22590
    65 125.16 1251.6 2689 18668
    70 127.07 1270.7 2782 15052
    75 128.98 1289.8 2880 12932
    80 130.89 1308.9 2977 10837
    85 132.80 1328.0 3079 9121
    90 134.70 1347.0 3180 7708
    95 136.60 1366.0 3285 6539
    100 138.50 1385.0 3390
    105 140.39 1403.9
    110 142.29 1422.9
    150 157.31 1573.1
    200 175.84 1758.4