    I wondered if anyone had a checklist or form for chiller commissioning. Well to be exact it's actually the water pump in the hydraulic system I need the checklist for, so I can be sure I haven't missed anything out.
    PS One of our guys had a look at a centrifugal fan on an air handler this morning, and says the airflow is really low. He's checked filters and everything else. I think the motor might be turning in reverse. Any other ideas ??
    a problem shared is a problem halved
    Aug 2005
    5,302
    Re: Screw Chiller commissioning
    If the fan does not have inlet dampers I would check the following.
    The first point is what you suggested. Fan rotation.
    Bad belt conditions (cracked, glazed, etc)
    Or, see if the fan has dirt built up in the vanes. I have seen a lot of centrifugal fans that accumulate dirt in the vanes. This can drastically reduce the airflow capability of the fans. It is not however much fun to clean these.
    Is the air system a constant volume system or variable volume system?
    Feb 2004
    Australia
    286
    21
    Hi US Iceman
    Variable system. The main thing I need your assistance with is commissioning the water (hydraulic system) pump. I guess the main thing is flow and return temps and pressures.
    Many Thanks
    James
    Feb 2004
    Australia
    286
    21
    Wish I had the time. If you send me the details then maybe it might be worth doing.
    Feb 2004
    Australia
    286
    21
    US ICEMAN
    Check your PM's
    11,024
    Airflow:- Have you checked for dropped fire dampers ?
    Water Pump:- Check electrics, check rotation, check valves, check water in system and all air out of system. Get flow data for commissioning valves and design flow rates. Check pump head against pump curve. Check running current. Balance system, record readings.
    Now start chiller but only if water flow rate is correct.
    ireland
    1,451
    41
    Had a centrif fan once that had been taken out to change bearings and then put back in upside down , ran for a year and 4 maintenances before it was spotted
    Al
    Feb 2004
    Australia
    286
    21
    Brian thank you.
    The only info I need is for the hydraulic pump, because I can't start up until I've got the water flow balanced. That should be fine. Many Thanks for the info.
  1. York Millenium Screw Chiller
    By iceman007 in forum Industrial Compressors
    Last Post: 15-01-2011, 11:56 PM
  2. flooded evaporator in screw chiller
    By Lc_shi in forum Technical Discussions
    Last Post: 05-07-2010, 05:37 AM
  3. York Screw Chiller How low will it go?????
    By bruceboldy in forum Industrial Compressors
    Last Post: 10-08-2007, 10:29 PM
  4. Mcquay PES Flooded Water Cooled Screw Chiller
    By Brian in forum Technical Speculations
    Last Post: 05-07-2006, 09:43 PM
  5. York Open Drive Screw Chiller
    By Cofreth in forum Air Conditioning
    Last Post: 24-10-2005, 02:17 PM