Results 1 to 8 of 8
  1. #1
    Join Date
    Feb 2004
    Location
    Australia
    Posts
    286
    Rep Power
    21

    Screw Chiller commissioning



    I wondered if anyone had a checklist or form for chiller commissioning. Well to be exact it's actually the water pump in the hydraulic system I need the checklist for, so I can be sure I haven't missed anything out.

    Thanks

    PS One of our guys had a look at a centrifugal fan on an air handler this morning, and says the airflow is really low. He's checked filters and everything else. I think the motor might be turning in reverse. Any other ideas ??


    a problem shared is a problem halved

  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Screw Chiller commissioning

    If the fan does not have inlet dampers I would check the following.

    The first point is what you suggested. Fan rotation.

    Bad belt conditions (cracked, glazed, etc)

    Or, see if the fan has dirt built up in the vanes. I have seen a lot of centrifugal fans that accumulate dirt in the vanes. This can drastically reduce the airflow capability of the fans. It is not however much fun to clean these.

    Is the air system a constant volume system or variable volume system?

  3. #3
    Join Date
    Feb 2004
    Location
    Australia
    Posts
    286
    Rep Power
    21

    Re: Screw Chiller commissioning

    Hi US Iceman

    Variable system. The main thing I need your assistance with is commissioning the water (hydraulic system) pump. I guess the main thing is flow and return temps and pressures.

    Many Thanks
    James
    a problem shared is a problem halved

  4. #4
    Join Date
    Feb 2004
    Location
    Australia
    Posts
    286
    Rep Power
    21

    Re: Screw Chiller commissioning

    Wish I had the time. If you send me the details then maybe it might be worth doing.
    a problem shared is a problem halved

  5. #5
    Join Date
    Feb 2004
    Location
    Australia
    Posts
    286
    Rep Power
    21

    Re: Screw Chiller commissioning

    US ICEMAN

    Check your PM's
    a problem shared is a problem halved

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Screw Chiller commissioning

    Airflow:- Have you checked for dropped fire dampers ?

    Water Pump:- Check electrics, check rotation, check valves, check water in system and all air out of system. Get flow data for commissioning valves and design flow rates. Check pump head against pump curve. Check running current. Balance system, record readings.

    Now start chiller but only if water flow rate is correct.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Screw Chiller commissioning

    Had a centrif fan once that had been taken out to change bearings and then put back in upside down , ran for a year and 4 maintenances before it was spotted

    Al

  8. #8
    Join Date
    Feb 2004
    Location
    Australia
    Posts
    286
    Rep Power
    21

    Re: Screw Chiller commissioning

    Brian thank you.

    The only info I need is for the hydraulic pump, because I can't start up until I've got the water flow balanced. That should be fine. Many Thanks for the info.
    a problem shared is a problem halved

Similar Threads

  1. York Millenium Screw Chiller
    By iceman007 in forum Industrial Compressors
    Replies: 26
    Last Post: 15-01-2011, 11:56 PM
  2. flooded evaporator in screw chiller
    By Lc_shi in forum Technical Discussions
    Replies: 25
    Last Post: 05-07-2010, 05:37 AM
  3. York Screw Chiller How low will it go?????
    By bruceboldy in forum Industrial Compressors
    Replies: 11
    Last Post: 10-08-2007, 10:29 PM
  4. Mcquay PES Flooded Water Cooled Screw Chiller
    By Brian in forum Technical Speculations
    Replies: 4
    Last Post: 05-07-2006, 09:43 PM
  5. York Open Drive Screw Chiller
    By Cofreth in forum Air Conditioning
    Replies: 4
    Last Post: 24-10-2005, 02:17 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •