    how inverters control condensation pressure ?



    Hello
    How an inverter split air conditioner is controlling the CP with its discharge, pipe, and ambient temperature sensors ?



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: how inverters control condensation pressure ?

    That will to a certain degree depend on what manufacturer you are looking at. Generally for modern equipment from the main manufacturers:

    - The discharge thermistor is used to protect the compressor from overheating by shutting the system down somewhere around 115-130ºC
    - The liquid line thermistor will vary the outdoor fan speed (And thus the head pressure whilst in cooling), unless there is a pressure transducer performing that task.
    - The ambient thermistor will prevent the unit from running outside it's design envelope but might also be used for other algorithms, like defrost control.



    .

  3. #3
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: how inverters control condensation pressure ?

    I was thinking almost so precisely too, thank you anyway.
    What actually caused me to ask is the diagnostic message (leds blinking ) on an Fujitsu inverter: "Cooling high pressure abnormal rise".
    Anything seems ok, only the condenser looked not to be very clean. But the fan was not speeding very high by that, what I would expect from the a/c algorythm in such case.

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: how inverters control condensation pressure ?

    You can get the fault sometimes because the coil is dirty but the 'air' sensor thinks that all is well.

    It can be fooled sometimes by putting the air sensor into the condenser coil fins so that it responds to the increased coil temperature. Not highly recommended though.
    Last edited by Brian_UK; 13-11-2012 at 12:21 AM.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: how inverters control condensation pressure ?

    Aha,
    Fujitsu....

    They were keeping to ambient temperature switching the outdoor fan from high to low until fairly recently.




    .

  6. #6
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: how inverters control condensation pressure ?

    Fijitsu "inverters" have BLDC motor fans.
    Unfortunately, almost solely the Daikin put out explicit descriptions of its products - most of other manufacturers go often very reserved on information concerning what they produce.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •