    Area of slot diffuser when calculate air flow during commissioning



    Now I am commissioning air flow balance, How can calculate area of slot diffuser?



  2. #2
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Area of slot diffuser when calculate air flow during commissioning

    contact manufacturer for free area.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Area of slot diffuser when calculate air flow during commissioning

    Make up an air collection hood and use that for measurements.

    Don't forget to calibrate it against a proven/measured airflow.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Apr 2009
    Location
    Panacea, Florida
    Age
    87
    Posts
    76
    Rep Power
    16

    Re: Area of slot diffuser when calculate air flow during commissioning

    r.bartlett is correct. The manufacturer will have a web site with diffuser technical catalogs and submittal sheets for free. Just google the manufacturer's name and the web site should be on the first search page. The engineering catalog will have all of the data on your diffuser, including free area, static and total pressure drop vs air flow, and throw vs air flow. You can usually download the catalog for future reference.

    As Brian noted, you will need an airflow measurement hood, such as those made by Alnor, to measure the airflow and compare it to the design.