    Daikin Altherma HT - how to set the room temperature to be more stabile



    I have the control unit in the room. It is set to 22°C. The problem (for me) is, that the temperature must drop for 0,5°C before system starts to heat, or it must be for 0,5°C above the actual setting before the system stops to heat.

    Can this hysteresis be smaller?



  2. #2
    Join Date
    Dec 2008
    Location
    UK
    Posts
    564
    Rep Power
    24

    Re: Daikin Altherma HT - how to set the room temperature to be more stabile

    I am sure that you can adjust the hysteresis to be a larger value but I am not aware that you can reduce it below 0.5°C. This would create short cycliing in the system, which could be counter productive.