Thread: Trane rtac 155 sensor bindinig
-
06-11-2012, 02:22 PM #1
Trane rtac 155 sensor bindinig
Hi guys
i am trying to replace faulty leaving water sensor in our chiller rtac 155.
I have downloaded tech view from trane site & installed.
When i click on the icon its not opening.
Does it open only after connecting to chiller processor.
Can we use usb adapter in place of rs232.
Pls send me ur valuable sugestions.
-
07-11-2012, 01:54 PM #2
Re: Trane rtac 155 sensor bindinig
Hi Anish,
You should be able to run Tech View with no unit connected.
If you cannot open program, then you have to uninstall and install again.
Be aware of minimum requirements that each version need and possible conflicts on your computer.
About USB to RS232 adapter. Use IOGEAR GUC232A. It is recommended, this and other two brands that I don’t remember, by Trane. (Not officially)
I have it, it works.
Regards,
CV
-
08-11-2012, 08:46 AM #3
Re: Trane rtac 155 sensor bindinig
hi buddy
As u said the latest version is not suporting my operating system(windows7 ulitma)
i tried with older version in another laptop. i found icon working.
i connected to the chiller display (dyns view ) procsseor through RS232 CABLE.
its showing CONNECTION FAIL .
-
08-11-2012, 02:22 PM #4
Re: Trane rtac 155 sensor bindinig
Hi Anish,
The cable should be direct and not cross over.
Direct means pin 1 to pin 1, pin 2 to pin 2 etc.
In cross over cables 2 pins are crossed.
Regards,
CV
-
16-11-2012, 05:38 AM #5
Re: Trane rtac 155 sensor bindinig
HI GUYS
Thank u Mr.Geardrive for support and advice.
The job was completed succesfully .
Problem was with computer operating system & soft ware tech -view was not supporting.
THANK U ALL ONCE AGAIN