    Condensing Unit Hermetic Compressor - Stalling and Tripping??



    Hi Everyone,
    Just looking at an Ice Cream Van with a small 1ph hermetic condensing unit (on R409A).
    The customer tells me a capacitor exploded and he replaced it, but fridge not cold.

    When I turn the unit on it starts ok and works for maybe a minute. Back Pressure falls Head pressure rises, all looks great, but then the compressor starts 'rumbling, and stalling' and after 10 - 15 secs, trips on the internal thermal overload.

    The capacitor looks fine, is the same rating 80mf. The relay is wired correctly. But the compressor is too hot for the work done when it cuts out. I've tested the windings (cold) ad they check out more or less ok, they pretty much add up.

    Any ideas???

    Cheers guys.
    FrenchFox.



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Condensing Unit Hermetic Compressor - Stalling and Tripping??

    When I turn the unit on it starts ok and works for maybe a minute. Back Pressure falls Head pressure rises,
    That's a good sign that you have a restriction somewhere in the unit. Have a good check up to find it.

  3. #3
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Condensing Unit Hermetic Compressor - Stalling and Tripping??

    Check motor current, to make sure the relay is dropping out start winding after startup.

  4. #4
    Join Date
    Aug 2012
    Location
    France
    Age
    56
    Posts
    9
    Rep Power
    0

    Re: Condensing Unit Hermetic Compressor - Stalling and Tripping??

    Good advice thanks.

  5. #5
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Condensing Unit Hermetic Compressor - Stalling and Tripping??

    80 uf is the start capacitor. There is a run capacitor to check as well.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Condensing Unit Hermetic Compressor - Stalling and Tripping??

    condenser coil, clean? fan working- wont be a weak klaxon, clip the running current, pot may be siezing