    York YCIV0590-1500 chiller trip on low suction superheat.



    Hi my name is joe, new to the forum so please advise me for the following,
    Checking a york chiller found trip on low suction superheat, later found out the level of the feeder tank was 3% when chiller had stoped, have a feeling is low in gas.
    thanks
    regards
    joe.



  2. #2
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    49
    Posts
    412
    Rep Power
    23

    Re: York YCIV0590-1500 chiller trip on low suction superheat.

    Quote Originally Posted by joe88 View Post
    Hi my name is joe, new to the forum so please advise me for the following,
    Checking a york chiller found trip on low suction superheat, later found out the level of the feeder tank was 3% when chiller had stoped, have a feeling is low in gas.
    thanks
    regards
    joe.
    hi joe, welcome to re.check the suction transducer and suction temp.sensor giving accurate output.

    Moideen-Dubai

  3. #3
    Join Date
    Sep 2009
    Location
    Cyprus
    Age
    65
    Posts
    110
    Rep Power
    15

    Re: York YCIV0590-1500 chiller trip on low suction superheat.

    Joe check your suction temperature sensor probably is the one that giving you that fault , and of course make sure the rest of the system is ok and you don't have any leakage

  4. #4
    joe88's Avatar
    joe88 Guest

    Re: York YCIV0590-1500 chiller trip on low suction superheat.

    well i checked the suction pressure with temperature, works on a 4 to 5k superheat on start up but later as other circuits starts the circuit working got to 50%of load and cause the suctuin pressure to rise, as so trips on suction super heat. Also checked the feeded levels on other circuits fount they are around 8%.

  5. #5
    Join Date
    Sep 2009
    Location
    Cyprus
    Age
    65
    Posts
    110
    Rep Power
    15

    Re: York YCIV0590-1500 chiller trip on low suction superheat.

    You have to check each system alone, because when the system is starting up needs about 20 min of running to establish a good ridding and that on full load , so if you have problems to run all the systems on full load , because lack of load , then you should run the systems one by one and wait about 20 min and then take the ridings, check also the sub cooling normally should be between 3-4 K, the superheat is between 5-6 K, but again this problem is caused because the drain valve stays to much open and the evaporator is filled with to much liquid causing low superheat temperature alarm, also you have the possibility if you go to the service mode you can check manually all the feed and drain valves

  6. #6
    Join Date
    Sep 2009
    Location
    Cyprus
    Age
    65
    Posts
    110
    Rep Power
    15

    Re: York YCIV0590-1500 chiller trip on low suction superheat.

    no ridings but readings

  7. #7
    joe88's Avatar
    joe88 Guest

    Re: York YCIV0590-1500 chiller trip on low suction superheat.

    Well i tried to check through the service mode, but couldnt change the levels, can i manually change the level of the feeder and drain tank ?

  8. #8
    Join Date
    Sep 2009
    Location
    Cyprus
    Age
    65
    Posts
    110
    Rep Power
    15

    Re: York YCIV0590-1500 chiller trip on low suction superheat.

    Joe to operate manually the feed and drain valves you need to know a passcode and you need to know the procedure, please don't ask me to give that code because i wont, but once your in abu dhabi and you cant find a solution to your problem, you can always call at york Qatar or Dubai .
    Also i will advies before start messing around with drains, feeds , sensors etc, i will strongly recommend , start to to check first the systems for any leaks etc, and like i said low suction temperature alarm mostly caused by the suction temperature sensor because this sensor is controlling the drain valve, also i will suggest if you have the possibility to make an operating print out and post it in here , one system at the time and on full load and like i said also you have to run the system at list for 20 min before you do anything

  9. #9
    joe88's Avatar
    joe88 Guest

    Re: York YCIV0590-1500 chiller trip on low suction superheat.

    Thank yorkman appreciated, i'll check for any leak in the system an also try to get the passcode.