    Pulling too many amps!



    I fitted a new Frascold single phase semi hermetic comp today , brand new, new contractor , switch gear all changed , compressor is taking overload out when switching over from start to run windings , I think it's the run capacitor ! Would like a second opinion :/) picking replacement capacitor tester tomorrow !!!!! Should be pulling 6.5 amps(run) ,pulling 12amps and rising !thanks in advance"



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Pulling too many amps!

    Both Phase and neutral are present and correct?
    Amp meeter functioning OK?
    Voltage as per COMPRESSOR marking plate?
    Amperage still twice of COMPRESSOR marking plate?

    Yepp, check your capacitors.



    .

  3. #3
    Join Date
    Sep 2008
    Location
    ENGLAND
    Age
    51
    Posts
    2
    Rep Power
    0

    Re: Pulling too many amps!

    Quote Originally Posted by The Viking View Post
    Both Phase and neutral are present and correct?
    Amp meeter functioning OK?
    Voltage as per COMPRESSOR marking plate?
    Amperage still twice of COMPRESSOR marking plate?

    Yepp, check your capacitors.



    .
    yip all meters are good , voltage ok , thanks for a third opinion . Had one of those days lol!

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Pulling too many amps!

    Also, is all wiring correct?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Mar 2010
    Location
    Australia
    Age
    44
    Posts
    3
    Rep Power
    0
    If all of the wiring is correct. Give it a dry run (no power to comp and check the resistance if that is ok. Check the microfarads of the capacitor using your multi metre. If that's ok check the windings with an ir tester if that's all good. It might be gas or system related check your pressures and make sure it's running the right pressures.

  6. #6
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Pulling too many amps!

    Over charged system will have these symptoms.
    Looks to me like you are looking for the key under the light, I believe that the problem is else where in the system.

  7. #7
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Pulling too many amps!

    Start relay not switching, or wired incorrectly.