    Question Desuperheater water flow control ideas



    For a heatpump project, I need to control the flow rate of hot water through a tube in tube desuperheater. Depending on the operating conditions, I need to regulate the hot water flow from 0.16 GPM to 1.5 GPM to heat it to 120°F. What are good ways to do this?



  2. #2
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Desuperheater water flow control ideas

    A temp driven regulator valve, can be a mechanical device or electro-mechanical device.

  3. #3
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Desuperheater water flow control ideas

    Would temp lags not perhaps come into play, here - especially with low flows?
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  4. #4
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Desuperheater water flow control ideas

    You might want to set up a face/bypass circuit where some of the water flows through a bypass, thus reducing the amount flowing through the heat exchanger.

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Desuperheater water flow control ideas

    You might find here what you are looking for
    http://www.watts.com/pages/learnAbou...s.asp?catId=64

  6. #6
    Join Date
    Apr 2010
    Location
    United States
    Posts
    17
    Rep Power
    0

    Re: Desuperheater water flow control ideas

    Thanks, chemi-cool. 131°F to eliminate Legionella Bacteria. There is not much penalty for this higher temperature because of the desuperheater counterflow design.

    Could someone suggest a specific regulator valve, perhaps with a face/bypass circuit for my application?

  7. #7
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,083
    Rep Power
    23

    Re: Desuperheater water flow control ideas

    http://www.solarnetix.com/solar-heat...mo-zone-valves would be a start then you need a controller for it. It will need P I & possibly a little D control. A three way valve will divert some of the flow for by-pass of de-superheater.

  8. #8
    Join Date
    Apr 2010
    Location
    United States
    Posts
    17
    Rep Power
    0

    Re: Desuperheater water flow control ideas

    Hi Tesla,

    It looks like the "3-Way Diverting Zone Valves from Belimo" is on/off only. How could I use it to regulate temperature with flow rate control?

  9. #9
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Desuperheater water flow control ideas

    Quote Originally Posted by Tesla View Post
    http://www.solarnetix.com/solar-heat...mo-zone-valves would be a start then you need a controller for it. It will need P I & possibly a little D control. A three way valve will divert some of the flow for by-pass of de-superheater.
    That used to be my old company......long gone (Solarnetix, not Belimo).

  10. #10
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Desuperheater water flow control ideas

    Quote Originally Posted by microHydro View Post
    Hi Tesla,

    It looks like the "3-Way Diverting Zone Valves from Belimo" is on/off only. How could I use it to regulate temperature with flow rate control?
    Nope, Belimo has modulation valves, look for 0-10vdc input. The valves and motor are separate. Danfoss also has a nice flow meter that can be inputted to a control to vary the valve based on flow and/or temp.

    Also:

    http://www.paw.eu/en/products/solar-...serstation.php

    It isn't exactly what you want but the idea behind it is to vary the speed of a pump based on the tank temp on the other side of a HX. This gives you stead state DHW from a dead water tank, and the parts inside this thing, and the controller, can do what you want. It may take a bit of experimentation tho....

  11. #11
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,083
    Rep Power
    23

    Re: Desuperheater water flow control ideas

    Sorry I just said it would be a start and Belimo has the valves and actuators to do it (from a quick google) - as stated correctly above (thanks Mike) 0 - 10vdc is the best option. That's where the PID control would come in for modulation. I was also thinking more like 1/2" or smaller depending on the application.

  12. #12
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Desuperheater water flow control ideas

    Maybe best to do a little sketch of what you intend for the application and what size is the refrig unit (heat pump)
    The application may determine that energy recovery is better than straight out temp recovery.

  13. #13
    Join Date
    Apr 2010
    Location
    United States
    Posts
    17
    Rep Power
    0

    Re: Desuperheater water flow control ideas

    I'd love some design wisdom! Here's the condenser and desuperheater section of the PID showing operating conditions for November. Refrigerant lines are black. The inlet red desuperheater water line is piped from the cold water inlet of a hot water tank. The red desuperheater outlet returns to the outlet of the hot water tank.
    Screen Shot 2012-10-29 at 10.44.02 PM.png
    Last edited by microHydro; 30-10-2012 at 05:53 AM.

  14. #14
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Desuperheater water flow control ideas

    If your draw, from the bottom and introduce back into the bottom via a sparge pipe and have a higher flow rate fixed, you will absorb more energy,
    But if you have enough hot water without an element, then the one pass method is OK.
    So what you could do on the cheap, is have a simple solenoid valve controlled by the outlet water temp, wait a bit more, there is a minimum flow device around solenoid valve that allows for the flow temp to be measured. I use 0.1L/M for this device (a long capillary tube works well)

  15. #15
    Join Date
    Apr 2010
    Location
    United States
    Posts
    17
    Rep Power
    0

    Re: Desuperheater water flow control ideas

    Thanks, Mad Fridgie
    The idea is that I will draw unheated water from the bottom of the hot water tank with a pump, and return the optimally heated water to the top of the hot water tank. An electric element may or may not be active.

    Please help me understand the operation of the solenoid valve topology. When the outlet temperature is low, the solenoid at the outlet closes. The capillary tube still flows hot water around the solenoid. When it is up to temperature, the solenoid opens. Have I got it?

  16. #16
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Desuperheater water flow control ideas

    In reverse,
    The sol valve control is correct (i have presumed that the water pump is off when the heat pump is off)

    The term optimally heated, can either be greatest amount of energy or required temp.