Thread: Pre Lube on Carrier 30GX
26-10-2012, 09:52 AM #1
Hello everyone,
I don't know if someone out there can help but I have a Carrier 30GX chiller which will not prelube.
I believe the oil pump is supposed to start before everything else fires up. This is not happening on one of the circuits. The control boards have been swapped, so I am confident that this is not the problem. What else could hold the pump off? There are no alarms so I presume this circuit is waiting for something like the oil temperature to be correct! The heater is working so I am at a bit of a loss.
Many Thanks
26-10-2012, 11:33 AM #2
Re: Pre Lube on Carrier 30GX
Does the pump work?
28-10-2012, 11:26 AM #3
There is no power to it, but I haven't connected it directly to a power supply. This is maybe something i can try first.
28-10-2012, 02:11 PM #4
OK Not.
So there is no power to the oil pump.
Follow the Link and a wiring diagram and legend will reveal that-
either your individual 110v transformer has failed or there is no output from terminal 9 = EP 7* output.
* is 1,2, 3 or 4. dependant upon which circuit is at fault ie EP72 is the oil pump for circuit 2.
Terminal 9 is on that circuits Compressor monitoring, control and safety module. A*c .
This circuit also flows through KM* Comp contactor and SP* HP switch.
So you should be able to trace your issue.
Good luck Grizzly
http://www.mediafire.com/?v57j5j15a5...bcj3a2j67o04xt
28-10-2012, 06:41 PM #5
Check the oil pump operation via quick test this will allow you to energise the oil pump and check electrical output to pump
30-10-2012, 01:41 PM #6
Hi Grizzly,
I am going to site tomorrow so will see if I can trace this through. I'll let you know how I get on.