    Does anyone know of a good calculation for BTUH to KWH? I have found some calcs that say .29 KWH per MBTU. NOt sure how accurate this is. A good calc will help me figure enrgy savings when I am asking for funding for projects.



  2. #2
    Join Date
    Jun 2008
    Location
    Finland
    Age
    45
    Posts
    34
    Rep Power
    0

    Re: BTU/H to KWH Conversion

    Hi

    this is from ashrae handbook : Btu/h x 0.2930711 = W/h
    Last edited by Teuria; 25-10-2012 at 02:30 PM.

  3. #3
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: BTU/H to KWH Conversion

    Coorsman777, just a very important correction:

    1) Btu.h?!? It doesn't exists. Btu/h exists and is the rate of energy per unit of time » power.

    2) Btu is already energy doesn't need be multiplied by h (time)

    3) kW.h is energy. kW is power. kW/h doesn't exists...doesn't make sense

    Teuria the correct answer is Btu/h x 0.2930711 = W.


    Many people do this error...
    To make progress is never good enough, I want to do better and better and better

  4. #4
    Join Date
    Jun 2008
    Location
    Finland
    Age
    45
    Posts
    34
    Rep Power
    0

    Re: BTU/H to KWH Conversion

    Quote Originally Posted by Sandro Baptista View Post
    Coorsman777, just a very important correction:

    1) Btu.h?!? It doesn't exists. Btu/h exists and is the rate of energy per unit of time » power.

    2) Btu is already energy doesn't need be multiplied by h (time)

    3) kW.h is energy. kW is power. kW/h doesn't exists...doesn't make sense

    Teuria the correct answer is Btu/h x 0.2930711 = W.


    Many people do this error...
    Hi

    Sorry my mistake.. i don't work with I-P units

    Btu/h x 0.2930711 = W
    But 1 Btu x 0.293071 = W.h (watt-hour)

    and this is again from ashrae handbook

  5. #5
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: BTU/H to KWH Conversion

    No problem!
    To make progress is never good enough, I want to do better and better and better

  6. #6
    Join Date
    Dec 2006
    Location
    Iran
    Age
    43
    Posts
    55
    Rep Power
    18

    Re: BTU/H to KWH Conversion

    Dear Friend,
    I think it would be better to check also http://www.engineeringtoolbox.com Also.