    cheese room problem.



    Hi guys, I'm after a bit of advice please.., I have a customer with a 10ft sq 7ft tall coldroom at +3C, the unit cools and defrosts perfectly.

    The problem I have is that the main side cover keeps getting forced off by icebuild up on tev and capillary tubes. I went to see the unit today to melt the ice and refit the cover but I was just wondering for possible causes/fixes...?



  2. #2
    Join Date
    Dec 2005
    Location
    South East England
    Age
    56
    Posts
    155
    Rep Power
    19

    Re: cheese room problem.

    I'm guessing that this coldroom has forced defrost (electric/hot gas)? You say that the evap. defrosts O.K. (which it would with forced defrost) but for the TEV to ice up in a coldroom that much is abnormal. To me it would indicate that the unit is running longer than normal due to excessive door opening/being left open for excessive periods or the system is running below par i.e. it's achieving setpoint but is running for abnormally long periods to achieve it.

  3. #3
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,119
    Rep Power
    26

    Re: cheese room problem.

    I think the evaporator is right near the door , near a hot kitchen, and with frequent door openings....
    Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.

  4. #4
    Join Date
    Jun 2005
    Location
    Stoke on Trent
    Age
    61
    Posts
    589
    Rep Power
    19

    Re: cheese room problem.

    The valve is staying open for too long, incorrect valve sizing, mis match of evap for application..........

  5. #5
    cuepower64's Avatar
    cuepower64 Guest

    Re: cheese room problem.

    Sounds to me like gas charge shortage or tev superheat setting incorrect

  6. #6
    Join Date
    Sep 2005
    Location
    Singapore
    Age
    59
    Posts
    145
    Rep Power
    19

    Re: cheese room problem.

    So which is the correct answer for this problem?

  7. #7
    Join Date
    Jun 2005
    Location
    Stoke on Trent
    Age
    61
    Posts
    589
    Rep Power
    19

    Re: cheese room problem.

    Quote Originally Posted by Cofreth
    So which is the correct answer for this problem?
    If it was me on site I would attach my gauges and see what the system is doing in relation to pressure & temperature, I would already of checked the obvious, evaporator fully flooding, expansion valve closing down and a clear sight glass, if all seemed well I would recalculate the duty of the room and re examine the selection and the match of the evaporator to the condensing unit for the application and check the sizing of the valve. It would probably be totally different if I was on site as I check things automatically, even small things like positioning of the valve bulb in the correct place and not half on a suction and on the edge of a bend or slightly raised from a proper contact due to a swaged joint or fitting, an experienced engineer would know exactly what I mean, something as simple as a poorly sited valve bulb hidden with armaflex tape can create the problems that you have raised. If the super heat has been messed with by another engineer, change the valve, resize the orifice and correctly fix the bulb. Give it a go.

  8. #8
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,119
    Rep Power
    26

    Re: cheese room problem.

    Andy W has got it about spot on.

    In fact Ive learnt from his very logical approach

    Thank You
    Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.

  9. #9
    Join Date
    Jun 2005
    Location
    Stoke on Trent
    Age
    61
    Posts
    589
    Rep Power
    19

    Re: cheese room problem.

    Quote Originally Posted by Aiyub
    Andy W has got it about spot on.

    In fact Ive learnt from his very logical approach

    Thank You
    I am in my 28 th year of refrigeration now, in that time I have experienced a lot of different problems and learnt through my own mistakes and mis diagnosis. Aiyub hit it on the head, logical approach.

  10. #10
    Join Date
    Oct 2002
    Location
    Hampshire
    Posts
    160
    Rep Power
    22

    Re: cheese room problem.

    Thank you very much for the advice/pointers guys, I really do appreciate it.

    I shall be going back to see the customer early next week to try and pinpoint this fault. When I was there the other week I did not really have a chance to make a proper diagnosis as the secretary that was there on here own wanted to get home and literally booted me out..

    I shall update the thread with my findings when I am allowed a bit more time to play.

    Once again, many thanks all and hope the new year treats you all well.
    regards...

  11. #11
    Join Date
    Aug 2005
    Location
    uk
    Posts
    46
    Rep Power
    0

    Re: cheese room problem.

    yes it may be shortages of gas and also in my experiences if the ambient temperature is very low ice will buid up in tev.

Similar Threads

  1. Strange problem
    By Peter_1 in forum Electrical
    Replies: 9
    Last Post: 10-04-2007, 05:19 PM
  2. Cool Room Problem
    By hybridjunction in forum Trouble Shooting
    Replies: 34
    Last Post: 31-01-2007, 12:09 PM
  3. Cheese Room Evaporator
    By Ireland in forum Technical Discussions
    Replies: 4
    Last Post: 05-04-2006, 11:22 PM
  4. Cheese Room Design 24V DC
    By jbelding in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2006, 03:23 PM
  5. Freezer Room Panels
    By Feeze in forum Technical Discussions
    Replies: 10
    Last Post: 22-04-2005, 05:58 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •