    Oct 2012
    Norway
    29
    2
    Vac pump on suction or discharge valve
    To create vacuum inside the compressor I was wondering if it is best to connect the vacuum pump to service valve on suction valve or service valve on discharge valve ?
    Or will it give the same result no matter which one I connect it to...
    How long time do I have to run the vac pump to make sure all air is out of the compressor housing.
    Thank u......
    Oct 2007
    manchester
    44
    5,707
    Re: Vac pump on suction or discharge valve
    vac on both sides for as long as possible, a torr gauge should be used to reach 500 microns or under 3 torr
    Oct 2012
    Norway
    29
    2
    OK thanks.
    But about these 2 service valves. Are they both connected to the inside of the compressor housing ? (Bitzer comp)
    It they are, then I guess it should be enough to vac. from only one of them.
    Or are the not having suction from the same area inside the compressor ?
    Sep 2003
    ISRAEL
    66
    4,173
    40
    There are valves inside the compressor, remember?
    Sep 2008
    430
    15
    If there are two service valves why not connect to them both? You`ll increase the vacuum flow and cut down the evacuation time.