Results 1 to 3 of 3
  1. #1
    Join Date
    Dec 2010
    Location
    brackenfell
    Posts
    18
    Rep Power
    0

    Newbie on split units



    Hi

    Newbie wanting to do things the right way. Could someone please help me with the right methods

    Would like to know what is the correct method of checking superheat on a split unit. I was also told the best way to charge a split unit is to put it on heating mode when you charge it,then you can never overcharge the unit. Is this true. That said if it provides heating and cooling. Otherwise you would charge it according to weight of gas....am i correct.

    Thanks



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: Newbie on split units

    With modern, inverter driven, splits you should always properly weigh the correct charge in to the system.

    And no, charging it in heating mode will not prevent you from overcharging it, sorry.



    .

  3. #3
    Join Date
    Dec 2010
    Location
    brackenfell
    Posts
    18
    Rep Power
    0

    Re: Newbie on split units

    Thanks Viking. Helps to know what the correct methods are.

Posting Permissions