Thread: BMS not picking up VSD fan
-
17-10-2012, 02:20 PM #1
BMS not picking up VSD fan
Hi
I have replaced a blown vsd drive with a new drive. Now the bms is not picking up the fan. Fan is running,but the bms is showing that it is tripped. I know that it is a parameter setting fault. Can anyone just help me out please!! Don't know which parameter to change.
Old drive: LS SV-iG5A 18.5kW
New drive: Yaskawa A1000 18.5kW
Siemens BMS
Regards
Johan
-
21-10-2012, 07:56 PM #2
Re: BMS not picking up VSD fan
Hi
are you using the relay outputs or the communication port?
try this :
http://www.yaskawa.com/site/products.nsf/products/Industrial%20AC%20Drives~A1000.html?openDocument&seq=1
best regardsTHE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
-
22-10-2012, 09:22 AM #3
Re: BMS not picking up VSD fan
Thanks for the link Goshen. I am using the ouput relays.
-
22-10-2012, 06:30 PM #4
Re: BMS not picking up VSD fan
HI
if that is the case, you should not have any problem configuring the outputs to do what you need .
good luckTHE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!