    Oct 2012
    Sri Lanka
    3
    How to determine cooling load of a chilled water cooled AHU?
    Hi All,
    If no heat recovery is available in the AHU, and if the AHU is supplied with centralized chilled water line for cooling and if the air flow from the AHU is known, the supply and the exhaust air temperatures are known, appreciate indicate procedure to calculate the cooling load of the chilled water cooled AHU.
    Thanks.
    moideen's Avatar
    Apr 2008
    u.a.e
    49
    412
    22
    Re: How to determine cooling load of a chilled water cooled AHU?
    Quote Originally Posted by Rohitha View Post
    Hi All,
    Thanks.
    4.5*CFM*ENTHALPY DEFFERENCE
    for example:
    Air quantity =370CFM
    Temperature of air entering the coil DB = 78F
    " WB = 67F
    Temperature of air leaving the coil DB = 59F
    " WB = 57F
    Enthalpy of air at 67F WB = 31.62 BTU/lb
    Enthalpy of air at 57F WB = 24.48 BTU/lb
    enthalpy deference = 7.14BTU/lb
    capacity = 4.5*370*7.14= 11888 BTU/lb
    Oct 2012
    Sri Lanka
    3
    Thanks and apprecite your reply
    Why do we mutiply by 4.5 ? and how the units of capacity become btu / lb , with air flow in CFM pls?
    Apr 2009
    Panacea, Florida
    87
    ∆Qs = ∆tdb * Cc * rho * cp * min/hr
    ∆Ql = ∆W * Cc * rho * QLV * min/hr
    ∆Qt = ∆h * Cc * rho * min/hr = ∆Qs + ∆Ql
    where (IP units)
    ∆Qs is the change in sensible heat of the flowing air (Btu/hr)
    ∆Ql is the change in latent heat of the flowing air (Btu/hr)
    ∆Qt is the change in total heat of the flowing air (Btu/hr)
    Cc is the air flow rate (ft3/min)
    W is the humidity ratio, lbs H20/lb dry air
    h is the enthalpy of the flowing air, btu/lb
    tdb is the dry bulb temperature of the flowing air, deg F
    rho is the average air density of the flowing air (lb/ft3)
    cp is the specific heat of air (Btu/lb/˚F)
    QLV is the latent heat of vaporization of water (Btu/lb H2O)
    for air at standard conditions: rho = .075, cp = .24, QLV = 1076
    ∆Qs = ∆tdb * Cc * 1.08
    ∆Ql = ∆W * Cc * 4840
    ∆Qt = ∆h * Cc *4.5
    Note that also, Qs + Ql = Qt
    The above from my PDH course
    HVAC Psychrometric Analysis to Avoid Moisture Problems, PDH course M409, www.pdhonline.org