Results 1 to 35 of 35
    Oct 2012
    Netherlands
    10
    Replacement R22 for NH3/CO2 or NH3
    Becouse of the new rules of the EU R22 is forbidden to use after 1-1-2015
    We have here 5 blast freezers (each one can hold 50 pallets double stack so 100 total) which uses R22.
    We have 2 mycoms running in our engine room to get a evaporate temperature around -27 degrees celcius at the 5 blast freezers.
    Now we have asked 2 contractor for a complete new installation.
    contractor 1 says go for NH3 with 2 Grasso V1100T total amount of 280KW
    2 pumps for circulation of the NH3 (makes it 300KW according the contractor)
    evaporate temperature -34 degrees celcius
    Condensation temperature 25 degrees celcius
    Contractor 2 says go for a NH3/CO2 system.
    Based on the same evaporate en condensation temperature as above.
    2 NH3 compressor OSKA7471/2 eco on 1 frame. (OSKA is Bitzer right?)
    3 CO2 compressor 4NHC -20/3 on 1 frame
    Both contractors are speaking for there own project.
    So we can't choose between both systeems.
    Constructor 1 says NH3 is the best
    Constructor 2 says NH3/CO2 is the best
    So our question is which one is the best in your eyes?
    1: Energy consumption
    2: Maintance.
    3: Difficulty to control the system
    4: Environment problems
    5: Building Difficulty for the constructor
    6: COP
    7: Safety for products and employers.
    8: Durability
    9: Suction or screw compressor
    10: Which system has the best build to upgrade in a later stadium?
    Jan 2010
    REPUBLIC OF SOUTH AFRICA
    Go for NH3, the best natural refrigerant for cold storage facilities. Worked on several CO2 plants in Africa on commercial level. You can't go wrong with NH3.
    Cool Is Good
    Sep 2003
    ISRAEL
    72
    4,248
    Re: Replacement R22 for NH3/CO2 or NH3
    How about cleaning the the system from mineral oil, replace the compressor and TXV and use R-507 instead?
    Oct 2012
    Netherlands
    10
    Well we don't want to use any CFK's (HCFK) for our new installation.
    And we are trying to get a lower energy consumption. And with R-507 or any other Refrigerants except NH3 or NH3/CO2 it wil increase our energy consumption by 10 til 25% in compare of R22
    So that's a no go.
    And the EU is ****ting around with there GWP list. R22 is now forbidden the next ones are already on the list.
    So we want to stick with futureproof refrigerant.
    Aug 2008
    Auckland
    55
    259
    21
    Not a Ammonia expert by any means, but your set up seems perfect for Ammonia.
    Don't know why the other contactor is trying to sell a hybrid NH3/Co2 system, more expensive to install, loss of efficiancy through the stage from NH3 to CO2.
    Aug 2009
    New Zealand
    2,554
    26
    Is your location industrial or commercial/residential.
    NH3 is great refrigerant, but is not so much human friendly! The NH3 system will have a large charge, so if there is a big leak, who and what will it effect. The combo system has a much reduced NH3 charge, so a lot less of an issue.
    Auckland
    74
    3,357
    37
    I have a preference for ammonia, being the efficiency of ammonia etc..and that the powers to be, cannot at this stage tax natural refrigerants. But dependent on site location local authourities take a dim veiw of ammonia in certain areas.
    Oct 2012
    Netherlands
    10
    Quote Originally Posted by mad fridgie View Post
    It's a industrial location.
    we use nh3 for almost 30 years in our normale warehouse.
    2000 kg of nh3 is used for that.
    And those compressors are still running smoothly and low maintance.. (Grasso's)
    Oct 2012
    Netherlands
    10
    Constructor said it's only using around 600 kg of NH3 if you go for complete NH3 installation. (and somehow i'm not sure about that 600 kg if the other old installation (30years) takes 2000 kg)
    Compare with i said here down below.. (other engine room has 2000kg of NH3) it's piece of cake then.
    Aug 2009
    New Zealand
    2,554
    26
    Charge does seem a bit low for a pump system.
    So your familiar NH3 and location is not an issue, So it must come down to capital cost and if they are close then a piece of cake it is!!
    Volvo245GLT's Avatar
    Volvo245GLT Guest
    Reclaim R22 and charge it up with R290 instead.
    No need to replace the oil or anything else, and energy efficiency will actually increase some.
    Aug 2008
    Auckland
    55
    259
    21
    Quote Originally Posted by Volvo245GLT View Post
    Sorry, I have to jump in here, ignore this fool. Retrofit to R290 (propane) with no other changes to the system? Here is the result from doing this stupidity!
    http://www.fire.org.nz/Media/News/20...-released.aspx
    Oct 2012
    Netherlands
    10
    Retrofitting isn't a option.
    They will all consume more power then the R22
    And indeed how stupid are people of getting propane?
    Nov 2009
    france
    64
    223
    Hi mjcornelissen,
    NH3 is the best choice for you. -34 is the uper limit for CO2 pumped and good COP/ammonia. the main difference is hot gaz defrost, easy with ammonia, much more difficult with Bitzer NHC (Tc max is +5°C). GRASSO V compressors have a very good efficiency and very low oil carry over.
    Oct 2008
    Colombia
    80
    Quote Originally Posted by mjcornelissen View Post
    1. OP1>Constructor 1 says NH3 is the best
    2. OP2>Constructor 2 says NH3/CO2 is the best
    1: Energy consumption >OP1
    2: Maintance.>OP1
    3: Difficulty to control the system> Unknow
    4: Environment problems > None
    5: Building Difficulty for the constructor >OP2
    6: COP : OP1
    7: Safety for products and employers. > OP2
    8: Durability >OP1
    9: Suction or screw compressor : What do you mean?
    10: Which system has the best build to upgrade in a later stadium? OP1
    Since contractors emit unsubstantiated opinions, I guess my opinions for or against either require no sustain (although facts exist).
    I think that the best choices favor the Contractor 1 in 5/2.
    Oct 2003
    5,630
    34
    MJ, zonder enige twijfel, NH3 en zeker niet CO2/NH3
    Oct 2012
    Netherlands
    10
    constructor 2 says he can get a 10% less energy consumption system then the old R22.
    constructor 1 is still counting how many % energy saving he will get in compare of the old R22
    There are several articles of dutch organisations which says you can get 15% till 30% less energy consumption in compare of a HFK system.
    Anyone has reached such numbers with new installations/plants?
    @ Peter can you give me some reasons/facts why to choose for NH3 and not CO2/NH3.
    Do you have experience with both systems?
    Oct 2008
    Colombia
    80
    Mr.Cornelissen:
    In regard to comparison between CO2 / NH3 system and pure NH3 two stages system, I may refer to an study by J.W. Pillis(1), presented in 2009 IIAR Conference , where conclusion are among other the following:
    CO2 cascade systems compared with two stage ammonia systems
    • CO2 cascade system demand more energy; the penalty for using CO2 cascade is about 13% at –20°F (–28.9 C) evaporating temperature;energy savings is not the reason to choose CO2 cascade over direct two-stage ammonia as it will almost always require additional power consumption.
    • CO2 Cascade’s low cycle efficiency, and the need for the cascade condenser with its unavoidable approach temperature, cause increased power consumption and a reduction in overall COP.
    Any more info I'll supply you by PM at your request,
    Josei
    (1)Energy Consumption with CO2/Cascade Systems by J.W. Pillis .Director Global Engineering – Refrigeration, Johnson Controls, Waynesboro, Pensylvania
    2009 Industrial Refrigeration Conference & Exhibition, International Institute of Ammonia Refrigeration
  19. #19
    Oct 2003
    5,630
    34
    MJ, I tjink Josei's post explains it' perfect. If you compare NH3 and R22, then you should also compare both refrigerants at the same working conditions. They mostly take in account low condenesing pressurs for NH3 due toe the evaporative condensors. But you then have to take teh same pressure also for R22. 15% is possible but 30% is exagerated.
    Anyhow, NH3 wil lrun at better COP's at the same conditions. NH32 is by far the best refrigerant thermodynamically seen.
    CO2/NH3 makes it much more prone to failures and the power needed will be higher. More difficult to service afterwards and you're stuck then also with you original contractor.
    Take proven technology since decades (!!)and choose for the setup with the lmeast chance for failures and the lowest power consumption: NH3.
  20. #20
    Auckland
    74
    3,357
    37
    Intergrate the existing two mycoms into site system. Load shedding at part load etc.,with cross over pipe work, swing compressors applications all on ammonia. Have a low side surge vessel and a high side chiller surge existing
  21. #21
    Aug 2009
    New Zealand
    2,554
    26
    A point I should have picked up earlier.
    The present system is on R22 Te is -27C, the NH3 system has a Te of -34C, are you changing the temp of your storage and processes.
    Does you present system do roughly what you require, if so and no other temp changes are required, why have the NH3 so low, is this purely to reduce the capital cost of the evaporators, I would ask at new figures where the Te on NH3 is -27C (capital will be higher, but long term efficiency will also be higher)
    On a very basic look at the design, by increasing you Te, your COP may go up by approx 0.5 . That is a big saving over 20 years.
  22. #22
    Oct 2012
    Netherlands
    10
    Well it takes several days (5) to freeze the products.. And we want to make it going faster. (4days)
    so quality is better and faster ready for shipment.
  23. #23
    Jan 2006
    Croatia
    68
    2,261
    31
    Hi, mjcornelissen
    Well it takes several days (5) to freeze the products.. And we want to make it going faster. (4days) so quality is better and faster ready for shipment.
    My suggestion is to go with NH3 .... and you cannot miss
    ... above you have all need answers .... just find someone to do the right job .... to choose good components and make a good installation...
    Best regards, Josip
  24. #24
    Aug 2009
    New Zealand
    2,554
    26
    And that makes perfect sense!
  25. #25
    Oct 2012
    Netherlands
    10
    1600 kg is the correct charge.
    The CO2/NH3 constructor 2 is going to make a offer for a NH3 installation instead of NH3/CO2.
    we have 2 appointment in the next weeks.
    constructor 1 had some cool news for us in regarding of the power consumption.. He will visit us to tell it.
    I will keep updating about this matter.
    BTW: Anyone wanna buy 2 mycoms R22
    Or anyone know a company's which will terminate the old installation? and probally ship to china or Africa for further freezing with R22 without EU rules
  26. #26
    Oct 2008
    Colombia
    80
    Some types of compressors Mycom R22 are convertible to NH3.
    Ask your distributor in Netherlands, could you use them in your projec
    t.
  27. #27
    Aug 2009
    New Zealand
    2,554
    26
    Glad to see the charge issue is sorted.
    It will be interesting to see what they say about energy use.
    Do you use hot water? If so ask for a heat recovery option. Also ask about about floating suction control?
    For example, you are in storage mode only (not freezing), you are able to drive your suction pressure up, saving even more energy.
    Is does come down to understanding your sites processes, electrical pricing structures.
  28. #28
    Oct 2003
    5,630
    34
    Let us know this 'cool' news
  29. #29
    3,356
    Sounds like a long time to blast freeze something!
    What are you freezing 7 how is it packed, most blast freezers of good design would be 24 hours. A carton tunnel in abbatoir on NH3 is 40 hours.
    Maybe a serious review of blast freezers could save a lot of time & power.
    Do you then have to store product for awhile or is it shipped straight away?
    If you have a good design then suction pressure can run higher which makes a massive difference to size & capacity of equipment as well as power consumed.
    Do you have description of the design etc?
  30. #30
    Auckland
    74
    3,357
    37
    Good point Ranger,
    the longer the freeze cycle the product quality reduces, perhaps blast freezing pre packaging, time to re-think the whole process. Also the mycom compresssor recip or screw can be adapted to ammonia from R22.
  31. #31
    Oct 2012
    Netherlands
    10
    constructor 1 made the visit.
    And it wil be around 10% till 15% less energy consumption compare to the old R22 installation.
    He even made a calculation about the NH3/CO2 installation and surprise: it will increase with 10% energy consumption compare the old R22 installation
    With the R22 on max capacity
    and the NH3 on 80% capacity so we have another 20% for expanding in the future.
    With this said.. Constructor 2 needs to explain his earlier 10% less energy consumption.
    We just received today his offer for a complete NH3 installation which we asked for.
    Didn't had time yet to review it.
    @josei.
    This was very helpfull. They even didn't know about this paper.
    More news coming soon.!
  32. #32
    Oct 2008
    Colombia
    80
    @josei.
    In regard to comparison between CO2 / NH3 system and pure NH3 two stages system, I may refer to an study by J.W. Pillis(1), presented in 2009 IIAR Conference...
    @mjcornelissen
    You are welcome , please spread kindly the knowledge about nh3 refrigeration, its energy savings and environment protection. A lot of engineer's analisys I have available to decision makers. You can see into my profile, colaborations that I worked before.
  33. #33
    Sep 2008
    Canada
    811
    As far as I remember Mr. Pillis compared only low sides of the plants. What about high sides?
  34. #34
    Oct 2008
    Colombia
    80
    Quote Originally Posted by Segei View Post
    @Segei What about high sides??
  35. #35
    Sep 2008
    Canada
    811
    When we talk about energy savings, we should compare energy efficiency of the whole(low sides and high sides) refrigeration plants. Mentioned technical paper was focused on energy efficiency of low sides of the refrigeration plants.
Tags for this Thread