Thread: cooling capacity
05-01-2006, 10:50 AM #1
cooling capacity
hi people ...
i need to calculate the cooling capacity for a refrigerant unit, the the compressor efficiency
so if you have an idea about this, inform me
thanks
05-01-2006, 02:45 PM #2
Re: cooling capacity
Ahmed,
The easiest way to do this is to use the compressor capacity from the manufacturer's catalog. After you have the performance data, you need to make sure you use the exact suction pressure and discharge pressure when referencing the catalogs. Convert the pressures into saturation temperatures, since this is what most manufacturers use in the rating tables.
If this is for your propane system, the curve I posted earlier will allow you do this.
With this you will have the compressor capacity and power (from the performance tables). You should also have the process cooling data (the heat load from the process). Someone at your facility should have this information.
The compressor capacity should be equal to or slightly exceed the process cooling load.
If you can obtain a computer printout of the compressor performance, the efficiencies are usually listed on the sheet.
What type of compressor do you have? Size, model numer, and manufacturer?
12-05-2010, 09:02 PM #3
Refrigernt cooling capacity
Hi, Just want to know how to measure and calculate the refrigerant cooling capacity. Can anyone give a hint?
Thanks,
12-05-2010, 09:22 PM #4
Hint: As an Engineer use the search facility here or on Google, also reading a Refrigeration book will provide immense knowledge.
13-05-2010, 03:25 AM #5
Brian_UK
you are so much he gentleman with these sorts of questions.
As well, I have applied your 100% work ethic principal, the wife is not happy as I am self employed.
R-407C and Coil Capacity
By glabah in forum RefrigerantsReplies: 5Last Post: 03-06-2006, 11:36 AM -
Cooling tower evaporation, blowdown, makeup and cycles
By miltbeychok in forum IndustrialReplies: 5Last Post: 14-10-2005, 06:34 PM -
By miltbeychok in forum FundamentalsReplies: 0Last Post: 13-10-2005, 05:14 AM -
TEV capacity related to pressure drop
By DaBit in forum CPU OverclockersReplies: 8Last Post: 06-12-2002, 05:11 PM -
Regulation of cooling capacity
By npaisnel in forum DomesticReplies: 13Last Post: 08-02-2002, 11:22 PM