    Daikin Altherma Pump Down?



    Hi to cut to the point next Friday 19-10-12 i have to move the outdoor unit to the floor as a customer is complaining the unit is vibrating through the house where its bolted to the wall
    Can you pump the system down like a AC Split? my background is mostly air con and fridge i have been on the altherma course a couple years ago so may have to dig my notes out but cant remember there being anything about pumping it down.

    Thanks in advance



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin Altherma Pump Down?

    Yes you can pump it down as normal....just make sure you drain the indoor unit first to prevent the plate heat exchanger freezing

  3. #3
    Join Date
    Apr 2011
    Location
    England
    Age
    35
    Posts
    41
    Rep Power
    0

    Re: Daikin Altherma Pump Down?

    Ok thanks i assume they all switch into cooling mode on the controller then?

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin Altherma Pump Down?

    No...there is a pump down button on the outdoor unit.

    We had a customer over in Shropshire that didn't pay his bill on time (we left it 4 months before we lost patience) so we travelled over early one morning, pumped his system down, loaded the outdoor unit onto our van and left before 5am.

    Needless to say, he paid the next day

  5. #5
    Join Date
    Dec 2010
    Location
    ZA
    Posts
    154
    Rep Power
    16

    Re: Daikin Altherma Pump Down?

    Hope you took 4 months t go back and put it in as well, and charged for the time and parts ( vacuum pump oil from NASA, went to ISS and back as well before you got it) at the right rate.

  6. #6
    Join Date
    Apr 2011
    Location
    England
    Age
    35
    Posts
    41
    Rep Power
    0

    Re: Daikin Altherma Pump Down?

    Haha good idea, thanks for the reply much appreciated

  7. #7
    Join Date
    Apr 2011
    Location
    England
    Age
    35
    Posts
    41
    Rep Power
    0

    Re: Daikin Altherma Pump Down?

    Job went lovely for a friday, didn't bother draining the indoor unit down in the end, didn't feel that it would be evaporating at a low enough temperature to freeze, even the power cable and transmission cables were long enough

    Thanks for the help guys