Thread: maneurop specs
    Feb 2009
    telford
    2,090
    33
    maneurop specs
    can anybody tell me the spec of a maneurop condensing unit model number mgz040c12e the horsepower is what i need and is it hbp/lbp/mbp thanks.
    Sep 2003
    ISRAEL
    72
    4,248
    Re: maneurop specs
    compressor on that unit is MTZ40, horse power is 3.5
    They dont make blue star anymore, now they are called optyma.
    4,713
    Re: maneurop specs
    I have similar data as per Chemi.
    The Dean and Wood catalogue. Pages 49 and 50.
    The new code is MGHD060HPC12E which is listed as 3hp 3ph?
    Best check with D&W Tech services!
    Sep 2003
    ISRAEL
    72
    4,248
    Re: maneurop specs
    Grizzly, MGH is for high ambient with MINERAL oil and compressor on that unit is MT36.
    The letter Z indicates POE oil.
    Depend of the refrigerant you use, [suitable for 134,404,507,407,22,12] it will go down as -40C evap. temp to 10C evap. temp.
    I use them for milk cooling at 0C evap and freezers at -30 evap.
    Feb 2009
    telford
    2,090
    33
    Re: maneurop specs
    thanks guys