    Earth tapped transformers



    Had a look at a Whirlpool Ice M/C today, the type that makes a block of ice that then slides onto a hot-wire cutting grid. The grid is powered at 20 volts from a step-down transformer. Now I think I've got a reasonable understanding of things electrical & even electronic -but what does the earth tapping part of the transformer do There was a live @ 230vac going in & the (I guess) 20vac live & neutral going to the cutting grid, but no neutral supply on the 230v side, just a cable going to earth from the windings


    Noah had to leave the dinosaurs behind as they would've sunk the boat.

  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Earth tapped transformers

    This sounds like an autotransformer where the secondary winding is part of the primary winding so as to give increased current capabilities to the lower voltage side. Have a look here http://ourworld.compuserve.com/homep...h/autoxfmr.htm or do a search for autotransformers

  3. #3
    Join Date
    Jan 2003
    Location
    Venezuela
    Posts
    58
    Rep Power
    22

    Re: Earth tapped transformers

    Quote Originally Posted by phil68
    Had a look at a Whirlpool Ice M/C today, the type that makes a block of ice that then slides onto a hot-wire cutting grid. The grid is powered at 20 volts from a step-down transformer. Now I think I've got a reasonable understanding of things electrical & even electronic -but what does the earth tapping part of the transformer do There was a live @ 230vac going in & the (I guess) 20vac live & neutral going to the cutting grid, but no neutral supply on the 230v side, just a cable going to earth from the windings


    As Frank says it is most likely an autotransformer. They are cheap, but not particular safe, as there are no isolation between primary and secondary side.

    A standard autotransformer (step down) is shown here.

    A________________C
    {
    {
    {
    {________D
    {
    {
    {
    B_______{


    If you have 130V between A-B, 20V between C-D and B is live and A neutral, then all is good and it will not kill you if you
    touch C or D.

    If, on the other hand, you connect the live to A and neutral to B, then C also will be live, and it is not safe to touch C or D. This
    possibility you can of course eliminated if you connect B to live and A to earth. Normally this would cause no trouble, but I am not sure if it is permitted to use earth as neutral in this way.

    Also, if the connection to A is open (blown fuse (fuses are not allowed here)) then again you have an unsafe situation.

    Saludos cordiales,

    Jan
    Last edited by PobodysNerfect; 04-01-2006 at 02:53 PM.

  4. #4
    Join Date
    Jan 2003
    Location
    Venezuela
    Posts
    58
    Rep Power
    22

    Re: Earth tapped transformers

    Sorry, my drawing went to hell.

    I hope all know how my transformer was supposed to look.

    Jan
    Attached Files Attached Files
    • File Type: doc A.doc (19.0 KB, 12 views)
    Last edited by PobodysNerfect; 04-01-2006 at 02:58 PM.

  5. #5
    Join Date
    Sep 2005
    Location
    Atlanta Georgia USA
    Age
    69
    Posts
    80
    Rep Power
    19

    Re: Earth tapped transformers

    phil68

    In the US many codes require the secondary of transformers be grounded.

    The primary and secondary are individual curcuits. You have to check phase to phase to get accurate readings.

    Steve Wright CM

  6. #6
    Join Date
    Mar 2004
    Location
    UK
    Posts
    624
    Rep Power
    21

    Re: Earth tapped transformers

    Hi

    Here,s some helpful info on whirlpool ice machines.

    www.truetex.com/icemachine.htm

    Regards Bernard

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Earth tapped transformers

    Good link Bernard but his methods for re-charging the unit -

Similar Threads

  1. Earth faults
    By reggie in forum Technical Speculations
    Replies: 17
    Last Post: 28-01-2006, 06:22 PM
  2. google earth.
    By Temprite in forum Computers & the Internet
    Replies: 1
    Last Post: 18-08-2005, 10:32 AM
  3. Earth continuity
    By bernard in forum Electrical
    Replies: 3
    Last Post: 04-04-2005, 06:35 PM
  4. 21st centry refrigeration system
    By dan wong in forum Technical Speculations
    Replies: 21
    Last Post: 20-04-2002, 12:30 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •