    Lennox chiller climatic controller alarm



    Can anyone help please I have alarm in my Lennox chiller using their Climatic DC50 controller.
    alarm shows NO LINK
    Can anyone help please.



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Lennox chiller climatic controller alarm

    comms link from unit to controller- easiest way is turn the unit off for 20 seconds, power it up, if it still shows no link then ur gonna haveto check the 6 core comms able to the controller- theres a rj45 telephone plug connections , also ensure the cable isnt near any power cables as it can ge interference,

  3. #3
    Join Date
    May 2008
    Location
    uae
    Age
    44
    Posts
    40
    Rep Power
    0

    Re: Lennox chiller climatic controller alarm

    we isolated power of the unit for maintance nearly 3 hrs later we on the power. after that it stared showing no link on display (DC 50 ). we checked for cable loose connection .
    we had spare controller connected we found disply back to normal.
    IS THIS THE PROBLEM WITH THE CONTROLLER OR THE COMMUNICATION CABLE .
    WE HAD PREVIOS HISTORY OF THIS UNIT HAVING THE SAME PROBLEM.

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Lennox chiller climatic controller alarm

    Anish.
    Install monkey has a valid point.
    Also is the controller plugged into J14? Which is for the DC50 and J15 is for the DS50!
    And J10 on your BM50 serial card?
    Just a thought.
    Grizzly

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Lennox chiller climatic controller alarm

    j10 on the bm50 (outstation) plugs onto the dt50 (amplifier board) then the dc50 plugs in on A
    ds50 (service tool) plugs in on C
    unplug ur dc50 test voltage on the 6 screw terminals
    0 +ve shield
    1 +vrl 30v dc
    2 grd
    3 rx-/tx-
    4 rx+/tx+
    5 grd
    6 +vrl 30vdc
    on the 2 pins ur getting 30vdc on plug in the cable for the dc50 and recheck ur 30vdc is still there- if not ur comms cable is grounding- check the connections at each end.
    the dc 50 can be hardwired in on the 1-6 screw termnals on the dt50.
    there are also some checks for a watchdog test to check the comms baud rate etc- will e mail you a manual for a pco controller and a chiller manual